    problem in ammonia thermosyphon system



    good after noon to all my refrigeration engineer frnds.Dear frnds i have 5 grasso screw comressors.one compresor -2 system ,1 for -10 ,1 for -30 system,2 for -38 system for their oil cooling i have given common header from ammonia thermosyphon reciever.all the compressor are running very well but in -10 system compressor the oil temp. goes suddenly high fron 45 degree celsius to 70 degree celsius and compressor goes trip.this problem takes place after 10 to 12 hour running.ammonia level in thermosyphon is sufficient,i also close all other oil cooler liquid supply valve shut off but i face same problem.please give yours valuable advise



  2. #2
    Join Date
    Jan 2008
    Location
    perth
    Age
    51
    Posts
    17
    Rep Power
    0

    Re: problem in ammonia thermosyphon system

    HI ghanghas, monitor the temperature of the thermosyphon in/out temp.
    Is this a new installation, or a previously o.k. system.
    Is there a balance line between the reciever and condenser.
    oil pump flow rate? slide valve behaviour?
    Im very keen to find out what is causing this.Please post what you find, I will talk with a friend tomorrow who has had a simmilar issue before.

  3. #3
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: problem in ammonia thermosyphon system

    I think there is oil in cooler with ammonia for 3 days this problem has happened in grasso compressor Gls 85 and i did that close inlet hand valve and outlet hand valve too there is drain valve in the bottom of the cooler joint it with a hose and other size of the hose to suction line to drain oil

Similar Threads

  1. oil recovery problem in ***** overfeed system
    By COLD WANG in forum Commercial
    Replies: 34
    Last Post: 05-11-2010, 10:14 AM
  2. Problem with freeze system on carpigiani machine
    By Ben Taylor in forum Trouble Shooting
    Replies: 6
    Last Post: 04-05-2009, 06:52 PM
  3. Problem with R409A system
    By bennybluetoes in forum Refrigerants
    Replies: 7
    Last Post: 11-01-2009, 04:48 AM
  4. Replies: 29
    Last Post: 02-10-2008, 09:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •