Results 1 to 23 of 23
    Jan 2010
    india
    35
    problem in ammonia thermosyphon system
    good after noon to all my refrigeration engineer frnds.Dear frnds i have 5 grasso screw comressors.one compresor -2 system ,1 for -10 ,1 for -30 system,2 for -38 system for their oil cooling i have given common header from ammonia thermosyphon reciever.all the compressor are running very well but in -10 system compressor the oil temp. goes suddenly high fron 45 degree celsius to 70 degree celsius and compressor goes trip.this problem takes place after 10 to 12 hour running.ammonia level in thermosyphon is sufficient,i also close all other oil cooler liquid supply valve shut off but i face same problem.please give yours valuable advise
    Jan 2010
    india
    35
    Re: problem in ammonia thermosyphon system
    Nov 2004
    China
    176
    Is the -10 compressor at the end of the thermosyphon header? Does it happen at night when your condensing pressure is probably lower? Can you post the Piping diagram or piping plan & section?
    Mar 2010
    Dammam
    83
    15
    yes, can you post your thermosyphon pipe route/diagrams specifically the sizes and elevations. The oil temp. goes high because there is insufficient heat exchange at your -10 comp. oil cooler.
    <"No one is so smart, they just stay with problems longer and use their imagination">
    Jan 2010
    india
    35
    Dear sir thanks for your reply it has been also takes place in day time after evevery 4 to 5 hours.i have one common header for thermosyphon oil cooling. on header one end is -38 degree compressors and other end -10 degree compressor.the temp. rise from 45 degree c to 70 degree c take place with in two minutes. while all the compressors have same line diagram.kindly give your valuable advise
    Jan 2010
    india
    35
    Quote Originally Posted by charlie n View Post
    Jan 2010
    india
    35
    Quote Originally Posted by ref717 View Post
    Jan 2010
    india
    35
    Quote Originally Posted by ghanghas85 View Post
    thermosyphon liquid supply header is 100 mm and return header is 125 mm, while oil cooler supply and return tappings are 50 mm and 65 mm respectively for 2 high stage compressor.
    Nov 2004
    China
    176
    Hard to analyze without installation drawings. It is sometimes possible to form a gas bubble in the supply header which can cause a backflow or at least a flow restriction. Supply header should rise at a slight angle in the direction of flow and the end of the header should be vented to the return header. (this is not always so simple to do. It depends on piping layout)
    Jun 2001
    N.Ireland
    1,630
    You should be running your oil between 70degc and 90 degc. The oil cooling is fine, your expectations are not.
    Kind Regards Andy
    Dec 2008
    usa
    83
    34
    Something is happening very fast to cause oil temperature to shoot up so quickly. I assume you have a three way oil temperature regulating valve. I suggest you check action of the three way oil regulating valve to see if it functioning properly. Could it be bypassing the hot oil around the oil cooler when it should be putting the hot oil through the oil cooler.
    Dec 2008
    usa
    83
    34
    Suddenly realized that your 70 C oil temperature is fairly common and normal. [I do not use Centigrade but that is not a valid excuse on my part.] I agree with Andy post. You are OK.
    3,356
    70-90 deg C oil temp is big news for me !
    Discharge temp would be interesting at these oil temps .
    If thats the case all his other machines -30C & -38C have a problem now with 45 C oil temp !
    Nov 2004
    China
    176
    I kind of agree with Ranger1. I like to see the oil between 50 and 65. (SCT+ 15 or 20) I think 45 is a little low but oil going to the compressor above 70 is going to give pretty high discharge temps.
    Aug 2007
    Adelaide Australia
    70
    562
    The recommended oil temp is 45 - 50 oC and the max oil temp is 80 oC, this is out of the Grasso manual.
    As Ranger1 said what happens to the discharge temp if your oil is 70 - 90oC.
    Charlie n could be on the right track.
    A piping layout would be helpful.
    Paul
    Mar 2003
    Australia
    11
    Does this occur when evaporators are being defrosted ? If you have large evaporators such as in a spiral freezer, when it goes on defrost it can cause a rapid fall in head pressure which can effect the thermosipon almost instantly.
    We had a plant that would do this when the production staff tried to defrost both spirals together, not enough evaporators in the rest of the system to supply enough hot gas and the machines would drop out on high oil temperature. If this is the case, reduce the amount of coil being defrosted at any one time.
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by Scott B View Post
    Yes Scott, I agree with you...but why doesn't happened the same with the -2ºC compressor system?
    Mar 2009
    U.S.A.
    320
    How large is the Min 10 Cmp compared to the Min 38 machine? Does the Thermosyphon Ht Exchanger sit higher on the Min 10 Machine?
    How is your condensing capacity controlled? Is there any substantial diversions for discharge gas on some form of on off control? As indicated, a large coil going into defrost will cause this but so will any condition that prompts a large and rapid change in discharge pressure or flow....Like a big heat reclaimer.
  19. #19
    Jan 2010
    india
    35
    Thanks for your suggestion actually i have connected both the supply and return line to the bottom of main thermosyphon supply and return header. My thermosyphon vessel bottom is just 620 mm below the condenser liquid outlet nozzle while in thermosyphon vessel 370 mm nozzle height for liquid outlet to high pressure .Todai i have observed that after some time there is no liquid ammonia flow through my oil cooler even i have closed all other oil cooler liquid supply valves closed.
  20. #20
    Jan 2010
    india
    35
    Quote Originally Posted by sterl View Post
  21. #21
    Jan 2010
    india
    35
    Quote Originally Posted by Sandro Baptista View Post
  22. #22
    Jan 2010
    india
    35
  23. #23
    Auckland
    74
    3,357
    37
    Your thermosyphon oil cooler should have around 2 metres liquid head to feed enough liquid for cooling. Can you raise the liquid level in the receiver, has system lost ammonia, the grassos from memory have small internal oil filters as well.
  1. oil recovery problem in ***** overfeed system
    By COLD WANG in forum Commercial
    Last Post: 05-11-2010, 10:14 AM
  2. Problem with freeze system on carpigiani machine
    By Ben Taylor in forum Trouble Shooting
    Last Post: 04-05-2009, 06:52 PM
  3. Problem with R409A system
    By bennybluetoes in forum Refrigerants
    Last Post: 11-01-2009, 04:48 AM
  4. Replies: 29
    Last Post: 02-10-2008, 09:48 PM