    Ammonia purging



    The below diagram is from a 1973 J&E Hall Info / defect Bulletin.

    Stating that in order to eliminate the possibility of introducing water into the compressor.
    Because as the pressure inside the crankcase of the compressor falls to ambient. The rate of absorption reduces the pressure in the crankcase very rapidly
    and water will enter the crankcase. (Yep been there!)

    The preferred solution is outlined below:-




    Explanation:-
    The gas should be vented into an enclosed vessel with a further outlet into a water container.
    The amount of water in the container would be less than that required to fill the enclosed vessel. This would then make it impossible for water to enter the crankcase.

    I have seen this type of arrangement recommended before but as yet don't know of anyone that applies it.
    Does anyone actually use anything like this out in the field?
    Grizzly

    PS hopefully the diagram is not to small for anyone to see? If it is left click on it and you will be redirected to a larger image!
    Just trying a newly recommended way of attachment.
    Last edited by Grizzly; 30-04-2010 at 11:37 PM.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Ammonia purging

    What a load of old rope. They at J&E H., had stars in there eyes obviously. No wonder they pailed into oblivion.

  3. #3
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Ammonia purging

    Yep been there too!! I worked for Halls for many many years & this method was never used, infact we were never encouraged to use it. Suppose they had to print something in their manuals

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Ammonia purging

    From my experience it only happens to you once in your career , unless you are a bit thick .
    Hopefully you get away with it not causing to much drama .
    Usually only happens when you turn off a hot compressor .
    Even if it is a good idea its something else you have to carry around .

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Ammonia purging

    Quote Originally Posted by RANGER1 View Post
    From my experience it only happens to you once in your career , unless you are a bit thick .
    Hopefully you get away with it not causing to much drama .
    Usually only happens when you turn off a hot compressor .
    Even if it is a good idea its something else you have to carry around .
    Wise words Ranger,
    Yep as you say I only did it once and then in my defence. I left a isolated compressor purging whilst being called away to an "emergency". On another site 30 mls away.
    Fortunatley I was purging a RC6311 to do a full overhall.
    So I had plenty of oppertunaty to dry it back out properly!
    As you say yet more to carry.
    Maggo, you could be correct. But back in those day they (J&E Hall) Had Ice Cream, Brewery Divisions etc.
    So they were large enough to fall fowl of the corporate bull **** that prevails in the larger comnpanies nowadays!
    What really killed Halls was fighting a hostile take over bid by Hanson Group ( but that's another story!)
    Pavillion.
    Bristol or Plymouth?
    Thanks for the input guys, I guess No body uses this type of system anywhere?
    Grizzly

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Ammonia purging

    Could you not just have a check valve in the purge hose?

    Not that i know anything about ammonia, i've only ever seen three ammonia comps, and that was in the 80's at the MMB depot in Felin Fach.

    Jon

  7. #7
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Ammonia purging

    Hi Grizzly

    I worked out of the Birmingham branch until 2004 when they centralised to Derby, didnt fancy that so threw the towel in, how about you have you worked for Halls?

    Pavilion

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Ammonia purging

    Hi Pavilion.
    Yep I used to work for Bristol latterly helping out on marine through Plymouth.
    Which I loved, but hated the commute.
    Hate won over love eventually!
    Grizzly
    PS I did not realise that Blue Yonder was in the midlands?
    Or maybe it isn't?

  9. #9
    Join Date
    Sep 2008
    Location
    Newcastle upon tyne
    Age
    75
    Posts
    80
    Rep Power
    16

    Re: Ammonia purging

    Hi

    also ex Halls but back in 70s

    used clear hose to see purging.

    isolate quick when water started reverse travel.

    Al

Similar Threads

  1. contaminants in ammonia systems
    By Johnny Rod in forum Refrigerants
    Replies: 29
    Last Post: 17-10-2011, 05:26 PM
  2. Want to be trained as an ammonia operator
    By Randy Williams in forum NH3
    Replies: 7
    Last Post: 26-11-2008, 08:15 PM
  3. Replies: 21
    Last Post: 03-02-2008, 05:10 PM
  4. Ammonia and CO2 reactor
    By gwapa in forum NH3
    Replies: 18
    Last Post: 07-01-2007, 04:50 PM
  5. New Ammonia Certification in United States
    By JerrydNH3 in forum NH3
    Replies: 11
    Last Post: 15-08-2006, 03:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •