    Question Cold Room



    Currently, I am working on refrigeration and do study’s at the same time to expand my knowledge. The more I know, the better service I can give to my clients.

    Could you assist me on the following questions please?

    How do I know what size compressor and coil do I have to use on different sizes cold rooms or freezer rooms? For example: My client asked me he wanted a freezer room, length 10m, width 6m, height 2.4m. This size is just an example.

    How do I know what size of liquid line and suction do I have to use on the above mentioned?

    How do I know at what settings do I set my LP / HP switch to on the above mentioned?

    What is the purpose of the solenoid on the liquid line? I assume it’s to cut off the gas, and then build up the pressure to the LP /HP switch, which is switching off the compressor. Is there any other reason for the solenoid? For example: Is the cold room switched off by the thermostat and do you still need the solenoid? If yes, why?

    I would really appreciate it if somebody can help me out with the correct info.

    Thanking you in advance for your time and help.

    Regards,
    Chris van der Walt
    South Africa
    E-Mail: cc.vanderwalt@gmail.com



  2. #2
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Cold Room

    Hi bro. Vanderwalt, if you're into ammonia refrigeration design and installation I strongly suggest that you should have your own Refrigeration handbook, codes and standards. The IIAR ammonia ref. piping handbook, ASHRAE handbook and ASME std. B31.5 would really help you in expanding your knowledge.

    As basics, to be able to know the compressor or condenser equipment size, you should first compute your Net refrigeration capacity for a specific room or system(Total room heat loads + Product load). From this, you can also properly select the size of your evaporator cooler.

    The liquid line solenoid valve is typical in all evaporator valve stations. This solenoid valve closes when your rm. temp reaches its required temp. as called by the rm. thermostat or temp. sensor. It will open as the temp. inside the rm. rises again. Nowadays, evaporator valve stations are also controlled by a PLC or SCADA system packaged with the whole ref. system.

    I hope I gave you an idea. Good luck in your career.
    <"No one is so smart, they just stay with problems longer and use their imagination">

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cold Room

    Quote Originally Posted by Chris- Africa View Post

    Could you assist me on the following questions please?
    http://www.refrigeration-engineer.co...ad.php?t=19701

    How do I know what size compressor and coil do I have to use on different sizes cold rooms or freezer rooms? For example: My client asked me he wanted a freezer room, length 10m, width 6m, height 2.4m. This size is just an example.
    Size of room doesn't mean anything without rest of required data for proper heat load calculation.
    http://www.refrigeration-engineer.co...ad.php?t=24673


    How do I know what size of liquid line and suction do I have to use on the above mentioned?
    You need to know required mass flow of refrigerant for required cooling capacity, than you could dimension pipes in that way that total pressure loss in them is satisfactory and at same time speed of refrigerant is OK for oil circulation.
    Buy some ASHRAE books.

    How do I know at what settings do I set my LP / HP switch to on the above mentioned?
    That depend on what is HP and LP pressure-stat is used for. If it is used as compressor protection than HP/LP is set in way that compressor does not operate outside of his operation limits.
    If LP is used as PUMP-DOWN control than it is set according to working pressures/temperatures.
    http://www.ra.danfoss.com/TechnicalI...chapter_03.pdf

    What is the purpose of the solenoid on the liquid line? I assume it’s to cut off the gas, and then build up the pressure to the LP /HP switch, which is switching off the compressor. Is there any other reason for the solenoid? For example: Is the cold room switched off by the thermostat and do you still need the solenoid? If yes, why?
    Purpose of solenoid is to cut refrigerant flow so that compressor suck all refrigerant after valve and when pressure is at level set by pump down LP switch compressor stop with operation. That way is ensured that at next start up of compressor there is no liquid at compressor suction. Thermostat operate solenoid valve and LP switch then switch OFF compressor. When temperature differential is passed, thermostats open, pressure rise and LP switch starts compressor.

    Research on Google with PUMP-DOWN keyword.
    Last edited by nike123; 01-05-2010 at 05:51 PM.

  4. #4
    Join Date
    Apr 2010
    Location
    Africa Refrigeration
    Age
    46
    Posts
    6
    Rep Power
    0

    Re: Cold Room

    Thanks for all the info!!!!!!!!!!!

Similar Threads

  1. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  2. Cold room floor
    By Andy AC in forum Commercial
    Replies: 8
    Last Post: 19-02-2009, 04:26 PM
  3. Cold room panels
    By LLCooLJ in forum Commercial
    Replies: 6
    Last Post: 07-04-2008, 04:18 PM
  4. cold room
    By CHILLED4 in forum Trouble Shooting
    Replies: 5
    Last Post: 16-11-2007, 11:44 PM
  5. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •