    Lightbulb Libert Hiross HPM



    Hello everyone,

    I'm studying new model of Hiross HPM for 1 month but I understand its control not too much (iCOM controller).

    We installed Hiross HPM with iCOM control to manage the dual cooling system (chilled water lead and compressor lag). Setpoint is 22 degC (+/-1 degC)and 50%RH (+/-10%RH).

    Problem
    The chilled water inlet is about 8 degC. Dehumidification system can control the humidity setpoint at 50%RH. However, the inlet changes to 12 degC, the humidity goes up to 70%RH - 80%RH and the compressors cannot start to dehumidify.

    Question
    Can I set any parameters in iCOM to control dehumidification by starting the compressors to help chilled water when the humidity is over the setpoint?

    Thanks,



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Libert Hiross HPM

    hi the answer is yes !
    you change the stage sp
    and the diffrential fo second stage to kick in,it is all in the manual ,
    so as said many times rtfm
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Libert Hiross HPM

    Is your chilled water pipework circuit design correct, does it include a buffer tank?

    Is there a steady load on the chiller or is the water temperature changing too quickly?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2010
    Location
    BKK, Thailand
    Posts
    10
    Rep Power
    0

    Re: Libert Hiross HPM

    Re: Brian

    Yes. The circuit is correct as design. Yes. We have a buffer tank.
    The water source from chiller changes from day time to another (small capacity) chiller at night time. So the water inlet rise from 8C to 12C.

    Re: goshen

    Could you tell me more clearly about 1st and 2nd stage setpoint?

    Thanks a lot,

  5. #5
    DavidJ's Avatar
    DavidJ Guest

    Re: Libert Hiross HPM

    Check line S419 - dehumidification enabled - Yes.
    Check line S130 - minimum CW temperature

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Libert Hiross HPM

    Quote Originally Posted by rinsoproud View Post
    Hello everyone,

    I'm studying new model of Hiross HPM for 1 month but I understand its control not too much (iCOM controller).

    We installed Hiross HPM with iCOM control to manage the dual cooling system (chilled water lead and compressor lag). Setpoint is 22 degC (+/-1 degC)and 50%RH (+/-10%RH).

    Problem
    The chilled water inlet is about 8 degC. Dehumidification system can control the humidity setpoint at 50%RH. However, the inlet changes to 12 degC, the humidity goes up to 70%RH - 80%RH and the compressors cannot start to dehumidify.

    Question
    Can I set any parameters in iCOM to control dehumidification by starting the compressors to help chilled water when the humidity is over the setpoint?

    Thanks,
    In order to dehumidify to 50%RH, the temp of the air as it leaves the coil must be 11K below the room temp. If the room temp is 22C, then the air off temp (measured close to the coil) must be 22-11=11C.

    If the water temp is 12C, it cannot possibly drop the air temp to 11C as it passes through the coil, therefore the humidity will be higher than 50%RH.
    Last edited by Gary; 04-05-2010 at 04:07 PM.

  7. #7
    Join Date
    Apr 2010
    Location
    BKK, Thailand
    Posts
    10
    Rep Power
    0

    Re: Libert Hiross HPM

    Thanks a lot, Gray!
    I will try to explain to my customer...

Similar Threads

  1. Hiross PIN Code
    By Whisty in forum Technical Discussions
    Replies: 18
    Last Post: 17-06-2011, 02:24 PM
  2. Liebert Hiross Close Control Humdifier bottles
    By moondawn in forum Air Conditioning
    Replies: 14
    Last Post: 08-08-2010, 08:00 AM
  3. Liebert Hiross super chiller
    By centrifugal in forum Trouble Shooting
    Replies: 0
    Last Post: 19-12-2009, 09:07 AM
  4. Literature on Stulz and Hiross ???
    By ArtMal2009 in forum Air Conditioning
    Replies: 1
    Last Post: 28-08-2009, 08:39 PM
  5. Hiross Hirange and Stulz literature
    By garyjh24 in forum Air Conditioning
    Replies: 2
    Last Post: 08-06-2008, 07:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •