    Effect of oversized condenser?



    Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????


    Q no 2) Secondly what will be the effect if a 2Ton compressor is used in a Ton system??



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Effect of oversized condenser?

    Quote Originally Posted by mianrizwan View Post
    Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????


    Q no 2) Secondly what will be the effect if a 2Ton compressor is used in a Ton system??
    1. low head pressure ,system will work unstable
    2. very hi head pressure,system will work unstable if the evaporator is small then you will be working on low suction as well- liquid slugging
    3. this is info offhand there will be many more symptomes!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Mar 2010
    Location
    pakistan
    Posts
    44
    Rep Power
    0

    Re: Effect of oversized condenser?

    oky thanks

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Effect of oversized condenser?

    Originally Posted by mianrizwan :
    Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????
    Goshen :
    low head pressure ,system will work unstable
    Can you perhaps expand more on this part - oversize condenser? The low head-pressure part, I understand.

    Where does the instability come from? Are you thinking on terms of driving pressure-difference across the orifice & possible hunting?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Sep 2005
    Location
    england
    Age
    41
    Posts
    21
    Rep Power
    0

    Re: Effect of oversized condenser?

    The system will be overcondensing resulting in an unstable supply of liquid at the tev inlet.
    Low head pressure without a c/fan spped controller can contribute to low pressure trips certainly on cold days.
    A 2 ton compressor on a 1 ton system will result in very high discharge pressure and overheating of the compressor providing it doesnt trip the HP safety first.
    Are these theoretical questions or are you building a system like this?

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Effect of oversized condenser?

    i hope not,!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  2. Condenser Temperature. HOW TO model it in 3D?
    By ruzfactor in forum Fundamentals
    Replies: 6
    Last Post: 07-09-2009, 10:57 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •