Results 1 to 11 of 11
    Sep 2009
    kampala
    9
    discharge pressure relife valve opening
    hi,
    i am using bitzer 6g.2 open type compressor for our chillroom,recently compressor getting over heat and internal pressure relife valve (bypassing)opening.crankcase also heating toomuch,interneal parts are ok.
    i try to replace new but still it is behaving same.
    expantion valve is Tex2(orifice 3).
    can any one help me to solve the problem.
    Govind
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    Re: discharge pressure relife valve opening
    Quote Originally Posted by govindarajan View Post
    hi,
    Govind
    what is the discharge pressur?
    check any referigerant restriction on dischrge line. ,discharge service valve or etc.
    Moideen-dubai
    495
    21
    Hi measure the temperature across the heads,the hottest one may have broken discharge valve or blowen gasket
    Sep 2009
    kampala
    9
    hi i opened all the heads found no damaged valves,but i have replaced one gasket and purged the condenser properly.
    Sep 2009
    kampala
    9
    hi all the line are open no restrictions,discharge pressure is 16bar&suction at 0.75bar.
    Oct 2009
    merida mexico
    282
    15
    relief valve is damaged. pressure to open the valve? high pressure switch must first open
    Apr 2001
    79
    5,071
    35
    What refrigerant are you using?
    3,856
    It should be R22 with a tex model txv.
    Jon
    Somerset
    69
    4,697
    Anyone else considering that there may be air in the system?
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    23
    hi govin,your comp.high pressure from discharge chamber does not run away to discharge line. Though your discharge service valve stem is fully back seated, if not moving valve inner device, then relief valve will be opened. check your service valve properly.
    Moideen-Dubai
    May 2006
    India
    74
    399
    Check the rating of safety valve.
    Since if it opens up at the given setting , it means pressure indeed is high . Have your presure gage (hp) checked up . Instead check why hp is shooting up ; find reasons .
    Besides check the safety valve for leak on its seat .
  1. Discharge pressure going very high in few seconds
    By Dhanasekar in forum Trouble Shooting
    Last Post: 17-04-2010, 03:39 PM
  2. Sporlan subcooling valve
    By BESC5240 in forum Technical Speculations
    Last Post: 13-10-2008, 03:23 PM
  3. Increasing Discharge pressure
    By mukunthavs in forum Trouble Shooting
    Last Post: 11-08-2008, 02:53 PM
  4. How to Design Refrigeration Systems
    By US Iceman in forum Fundamentals
    Last Post: 24-07-2008, 04:27 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Last Post: 02-10-2007, 10:18 PM