discharge pressure relife valve opening
hi,
i am using bitzer 6g.2 open type compressor for our chillroom,recently compressor getting over heat and internal pressure relife valve (bypassing)opening.crankcase also heating toomuch,interneal parts are ok.
i try to replace new but still it is behaving same.
expantion valve is Tex2(orifice 3).
can any one help me to solve the problem.
Thanks
Govind
-
29-04-2010, 09:15 AM #2
-
29-04-2010, 07:42 PM #3
Re: discharge pressure relife valve opening
Hi measure the temperature across the heads,the hottest one may have broken discharge valve or blowen gasket
-
30-04-2010, 05:55 AM #4
Re: discharge pressure relife valve opening
hi i opened all the heads found no damaged valves,but i have replaced one gasket and purged the condenser properly.
-
30-04-2010, 05:57 AM #5
Re: discharge pressure relife valve opening
hi all the line are open no restrictions,discharge pressure is 16bar&suction at 0.75bar.
-
30-04-2010, 03:57 PM #6
Re: discharge pressure relife valve opening
relief valve is damaged. pressure to open the valve? high pressure switch must first open
-
30-04-2010, 04:36 PM #7
Re: discharge pressure relife valve opening
What refrigerant are you using?
-
30-04-2010, 08:31 PM #8
-
30-04-2010, 09:02 PM #9
Re: discharge pressure relife valve opening
Anyone else considering that there may be air in the system?
Grizzly
-
01-05-2010, 05:57 AM #10
Re: discharge pressure relife valve opening
hi govin,your comp.high pressure from discharge chamber does not run away to discharge line. Though your discharge service valve stem is fully back seated, if not moving valve inner device, then relief valve will be opened. check your service valve properly.
Moideen-Dubai
-
05-05-2010, 11:26 AM #11
Re: discharge pressure relife valve opening
Check the rating of safety valve.
Since if it opens up at the given setting , it means pressure indeed is high . Have your presure gage (hp) checked up . Instead check why hp is shooting up ; find reasons .
Besides check the safety valve for leak on its seat .
Similar Threads
-
Discharge pressure going very high in few seconds
By Dhanasekar in forum Trouble ShootingReplies: 19Last Post: 17-04-2010, 03:39 PM -
Sporlan subcooling valve
By BESC5240 in forum Technical SpeculationsReplies: 8Last Post: 13-10-2008, 03:23 PM -
Increasing Discharge pressure
By mukunthavs in forum Trouble ShootingReplies: 2Last Post: 11-08-2008, 02:53 PM -
How to Design Refrigeration Systems
By US Iceman in forum FundamentalsReplies: 63Last Post: 24-07-2008, 04:27 PM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM