    discharge pressure relife valve opening



    hi,

    i am using bitzer 6g.2 open type compressor for our chillroom,recently compressor getting over heat and internal pressure relife valve (bypassing)opening.crankcase also heating toomuch,interneal parts are ok.
    i try to replace new but still it is behaving same.
    expantion valve is Tex2(orifice 3).
    can any one help me to solve the problem.

    Thanks
    Govind



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: discharge pressure relife valve opening

    Quote Originally Posted by govindarajan View Post
    hi,

    i am using bitzer 6g.2 open type compressor for our chillroom,recently compressor getting over heat and internal pressure relife valve (bypassing)opening.crankcase also heating toomuch,interneal parts are ok.
    i try to replace new but still it is behaving same.
    expantion valve is Tex2(orifice 3).
    can any one help me to solve the problem.

    Thanks
    Govind
    what is the discharge pressur?
    check any referigerant restriction on dischrge line. ,discharge service valve or etc.

    Moideen-dubai
    Last edited by moideen; 01-05-2010 at 05:16 AM. Reason: mistake

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: discharge pressure relife valve opening

    Hi measure the temperature across the heads,the hottest one may have broken discharge valve or blowen gasket

  4. #4
    Join Date
    Sep 2009
    Location
    kampala
    Posts
    9
    Rep Power
    0

    Re: discharge pressure relife valve opening

    hi i opened all the heads found no damaged valves,but i have replaced one gasket and purged the condenser properly.

  5. #5
    Join Date
    Sep 2009
    Location
    kampala
    Posts
    9
    Rep Power
    0

    Re: discharge pressure relife valve opening

    hi all the line are open no restrictions,discharge pressure is 16bar&suction at 0.75bar.

  6. #6
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: discharge pressure relife valve opening

    relief valve is damaged. pressure to open the valve? high pressure switch must first open

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: discharge pressure relife valve opening

    What refrigerant are you using?

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: discharge pressure relife valve opening

    Quote Originally Posted by Gary View Post
    What refrigerant are you using?
    It should be R22 with a tex model txv.

    Jon

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: discharge pressure relife valve opening

    Anyone else considering that there may be air in the system?
    Grizzly

  10. #10
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: discharge pressure relife valve opening

    Quote Originally Posted by govindarajan View Post
    hi all the line are open no restrictions,discharge pressure is 16bar&suction at 0.75bar.
    hi govin,your comp.high pressure from discharge chamber does not run away to discharge line. Though your discharge service valve stem is fully back seated, if not moving valve inner device, then relief valve will be opened. check your service valve properly.
    Moideen-Dubai

  11. #11
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: discharge pressure relife valve opening

    Check the rating of safety valve.
    Since if it opens up at the given setting , it means pressure indeed is high . Have your presure gage (hp) checked up . Instead check why hp is shooting up ; find reasons .
    Besides check the safety valve for leak on its seat .

Similar Threads

  1. Discharge pressure going very high in few seconds
    By Dhanasekar in forum Trouble Shooting
    Replies: 19
    Last Post: 17-04-2010, 03:39 PM
  2. Sporlan subcooling valve
    By BESC5240 in forum Technical Speculations
    Replies: 8
    Last Post: 13-10-2008, 03:23 PM
  3. Increasing Discharge pressure
    By mukunthavs in forum Trouble Shooting
    Replies: 2
    Last Post: 11-08-2008, 02:53 PM
  4. How to Design Refrigeration Systems
    By US Iceman in forum Fundamentals
    Replies: 63
    Last Post: 24-07-2008, 04:27 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •