    Smile Bench testing semi hermetic compressors



    Hello,
    can any one tell me how many bench tests can be done on semi hermetic compressors without
    using *****, from 3hp up to 60 hp
    thanks !!



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Bench testing semi hermetic compressors

    Quote Originally Posted by Ed Fitz View Post
    Hello,
    can any one tell me how many bench tests can be done on semi hermetic compressors without
    using *****, from 3hp up to 60 hp
    thanks !!

    They run them for a short period of time on OFN (nitrogen).

    They do not run them for too long because they overheat but they have a big rig that lets them
    connect up.

    taz

    .

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bench testing semi hermetic compressors

    Yes, manufacturer of compressors test them with OFN shortly.

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Bench testing semi hermetic compressors

    Are you sure?

    I don't think I would run a comp with nitrogen in it.
    A small comp will not be able to compress it.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Bench testing semi hermetic compressors

    Quote Originally Posted by chillin out View Post
    Are you sure?

    I don't think I would run a comp with nitrogen in it.
    A small comp will not be able to compress it.

    Chillin
    They can compress it, its squishy cos its a gas, the problem comes in a fridge system because they can't condence it hence a stupid high discharge pressure in no time.
    On a specially designed test rig it would be ok, it would just measure flow, pressure and run current etc and compare to a new comp specs.

    Jon

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bench testing semi hermetic compressors

    A compressor compresses whatever gas it sucks. Why shoudn't it be able to compress it?
    Surely, the max ratio depends on the compressor, though...

    The way it works is exactly as monkey spanners explained. It's not tested on a condensing unit.

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Bench testing semi hermetic compressors

    hi all , AIREDALE the yorkshire based a-c manufatorer test runs there units on ofn

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Bench testing semi hermetic compressors

    The important test is the leak back test which sets a limit for the discharge reed valves to suction valve reed . Do not run semi-hermetic comp on N2 . Do a free run test . The compressor builds up an air pressure of say 120 psig in a receiver tanks , switch off the compressor & measure leak back flow .

  9. #9
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Bench testing semi hermetic compressors

    MR dd KORANNE, YOU ARE RIGHT do not use N2 on any fridge compressor, use OFN, THAT IS OXYGEN FREE NITROGEN

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Bench testing semi hermetic compressors

    Quote Originally Posted by D.D.KORANNE View Post
    The important test is the leak back test which sets a limit for the discharge reed valves to suction valve reed . Do not run semi-hermetic comp on N2 . Do a free run test . The compressor builds up an air pressure of say 120 psig in a receiver tanks , switch off the compressor & measure leak back flow .
    No. Don't follow this advice. Semi recips for refrigeration and air conditioner shall never be pumping air.

Similar Threads

  1. (semi) Hermetic vs Open drive compressors
    By emlotte in forum Technical Speculations
    Replies: 1
    Last Post: 05-11-2009, 03:55 PM
  2. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 10:36 PM
  3. Dorin Semi hermetic Compressor
    By Samarjit Sen in forum Industrial Compressors
    Replies: 5
    Last Post: 02-07-2007, 04:06 PM
  4. do we need a hermetic or semi hermetic comp.?
    By duraid in forum Fundamentals
    Replies: 14
    Last Post: 17-04-2007, 05:52 PM
  5. Part Wound Semi Hermetic Compressors
    By bernard in forum Electrical
    Replies: 9
    Last Post: 22-12-2005, 06:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •