    Hello,
    can any one tell me how many bench tests can be done on semi hermetic compressors without
    using *****, from 3hp up to 60 hp
    thanks !!
    Oct 2006
    1,843
    21
    Re: Bench testing semi hermetic compressors
    Quote Originally Posted by Ed Fitz View Post
    Hello,
    thanks !!
    They run them for a short period of time on OFN (nitrogen).
    They do not run them for too long because they overheat but they have a big rig that lets them
    connect up.
    taz
    Mar 2006
    Merate (LC) - Italy
    2,549
    Yes, manufacturer of compressors test them with OFN shortly.
    Oct 2004
    Scotland
    1,454
    21
    Are you sure?
    I don't think I would run a comp with nitrogen in it.
    A small comp will not be able to compress it.
    Chillin
    and go get a cuppa
    3,853
    Quote Originally Posted by chillin out View Post
    Are you sure?
    Chillin
    They can compress it, its squishy cos its a gas, the problem comes in a fridge system because they can't condence it hence a stupid high discharge pressure in no time.
    On a specially designed test rig it would be ok, it would just measure flow, pressure and run current etc and compare to a new comp specs.
    Jon
    Mar 2006
    Merate (LC) - Italy
    2,549
    A compressor compresses whatever gas it sucks. Why shoudn't it be able to compress it?
    Surely, the max ratio depends on the compressor, though...
    The way it works is exactly as monkey spanners explained. It's not tested on a condensing unit.
    Oct 2008
    mallorca, spain,
    75
    768
    hi all , AIREDALE the yorkshire based a-c manufatorer test runs there units on ofn
    May 2006
    India
    74
    399
    The important test is the leak back test which sets a limit for the discharge reed valves to suction valve reed . Do not run semi-hermetic comp on N2 . Do a free run test . The compressor builds up an air pressure of say 120 psig in a receiver tanks , switch off the compressor & measure leak back flow .
    Oct 2008
    mallorca, spain,
    75
    768
    MR dd KORANNE, YOU ARE RIGHT do not use N2 on any fridge compressor, use OFN, THAT IS OXYGEN FREE NITROGEN
    Mar 2006
    Merate (LC) - Italy
    2,549
    Quote Originally Posted by D.D.KORANNE View Post
    No. Don't follow this advice. Semi recips for refrigeration and air conditioner shall never be pumping air.
  1. (semi) Hermetic vs Open drive compressors
    By emlotte in forum Technical Speculations
    Last Post: 05-11-2009, 03:55 PM
  2. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Last Post: 27-01-2009, 10:36 PM
  3. Dorin Semi hermetic Compressor
    By Samarjit Sen in forum Industrial Compressors
    Last Post: 02-07-2007, 04:06 PM
  4. do we need a hermetic or semi hermetic comp.?
    By duraid in forum Fundamentals
    Last Post: 17-04-2007, 05:52 PM
  5. Part Wound Semi Hermetic Compressors
    By bernard in forum Electrical
    Last Post: 22-12-2005, 06:33 PM