    Maximum Starting Current



    Dear all,

    Please help me on the following:

    What is the maximum starting current of a system (AHU connected to two condenser units) if we know the maximum starting current of each component:

    Maximum starting current of evaporator fan = 74 Amp

    Maximum starting current of condenser fan = 21.75 Amp (Number = 2 condenser fans)

    Maximum starting current of compressor = 125 Amp (Number = 2 compressors)

    Is the maximum starting current equals the total of maximum starting current of each component?

    Thanks.



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Maximum Starting Current

    Hi as a rule of thumb the answer is yes!
    if u have inverter compressors or fans the picture is different.
    it would be recomended to start componnents one at a time .
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Nov 2009
    Location
    Malaysia
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: Maximum Starting Current

    Meaning, the maximum starting current is 367.5 Amp..

    Seems like the amp is a bit outrageous..

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Maximum Starting Current

    Your maximum is 125amp as stated by yourself.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Maximum Starting Current

    Depending on sequence of turning ON of electric loads, maximum starting current is sum of running current of already turned on loads and starting current of load which is currently on starting.

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Scroll compressor current
    By Scott Buker in forum New Technologies
    Replies: 2
    Last Post: 02-10-2009, 11:54 PM
  3. Motor Current Fault York RecipPak YCUZ880E8
    By iaHVACguy in forum Trouble Shooting
    Replies: 0
    Last Post: 23-07-2009, 02:58 PM
  4. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM
  5. current draw on condenser fan motor
    By dan wong in forum Trouble Shooting
    Replies: 15
    Last Post: 25-05-2001, 06:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •