What is the maximum starting current of a system (AHU connected to two condenser units) if we know the maximum starting current of each component:
Maximum starting current of evaporator fan = 74 Amp
Maximum starting current of condenser fan = 21.75 Amp (Number = 2 condenser fans)
Maximum starting current of compressor = 125 Amp (Number = 2 compressors)
Is the maximum starting current equals the total of maximum starting current of each component?
Thanks.
-
28-04-2010, 05:06 AM #2
Re: Maximum Starting Current
Hi as a rule of thumb the answer is yes!
if u have inverter compressors or fans the picture is different.
it would be recomended to start componnents one at a time .THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
28-04-2010, 05:49 AM #3
Re: Maximum Starting Current
Meaning, the maximum starting current is 367.5 Amp..
Seems like the amp is a bit outrageous..
-
28-04-2010, 11:45 PM #4
Re: Maximum Starting Current
Your maximum is 125amp as stated by yourself.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-04-2010, 04:15 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Maximum Starting Current
Depending on sequence of turning ON of electric loads, maximum starting current is sum of running current of already turned on loads and starting current of load which is currently on starting.
Similar Threads
-
Carrier Transicold Container Problem
By Shamel in forum TransportReplies: 39Last Post: 23-01-2012, 11:23 PM -
Scroll compressor current
By Scott Buker in forum New TechnologiesReplies: 2Last Post: 02-10-2009, 11:54 PM -
Motor Current Fault York RecipPak YCUZ880E8
By iaHVACguy in forum Trouble ShootingReplies: 0Last Post: 23-07-2009, 02:58 PM -
Starting a compressor, and receiver questions.
By DaBit in forum Technical SpeculationsReplies: 9Last Post: 24-08-2002, 12:37 PM -
current draw on condenser fan motor
By dan wong in forum Trouble ShootingReplies: 15Last Post: 25-05-2001, 06:12 AM