27-04-2010, 01:48 PM #1
R410A leakage
System -Daikin VRV III,Outdoor model -RXYQ18PY,Indoor model -FXFQ100PVE
What is the easy way to check the R410 leakage ? Is there is any error code for decrease in pressure? then how to find it.
-
27-04-2010, 02:42 PM #2
Re: R410A leakage
Weigh out the charge and compare it to initial charge there is no quick fix!
-
27-04-2010, 04:47 PM #3
Re: R410A leakage
Providing that the system comissioning was done correctly i.e autocharge function,full learning curve were carried out the VRVIII can perform a refrigerant containment check then using the binary codes you can work out the amount lost but if the system does have a leak on it you need to carry out recovery setting and pull the gas and pressure test.
follow this link
www.extranet.daikin.co.uk
for the service manuals for this kit it'll tell you how to carry out the above functions
Si34-601 should be the manual you require
edit: use http://extranet.daikin.co.uk , but you will need to register on the site.Last edited by Brian_UK; 27-04-2010 at 10:41 PM. Reason: Corrected URL, Brian
-
28-04-2010, 07:58 AM #4
Re: R410A leakage
You may be able to get some indication from the service code 41, which wil give an indication of the air and coil temperatures. If the system is short of refrigerant there should be a noticeable difference in values when compared to the expected or previously observed. However if the system is only slightly short, the temperature may still be acceptable. Only sure way is to reclaim and weigh the refrigerant as previously suggested.
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.
Similar Threads
-
Pipes to large for R410a??
By Spanglishsparky in forum Technical SpeculationsReplies: 6Last Post: 09-05-2009, 12:57 AM -
My freezer inner pipe leakage
By syaful in forum DomesticReplies: 3Last Post: 05-03-2009, 10:52 AM -
Pressure Testing for R410a
By Pooh in forum Tools and CalculatorsReplies: 33Last Post: 13-08-2008, 11:41 PM -
R410A pressure in air conditioning
By irwinchong80 in forum Technical DiscussionsReplies: 4Last Post: 06-10-2007, 07:33 PM -
R410A captube sizing for 2.5 bar / 35 psi pressure drop
By DaBit in forum Technical SpeculationsReplies: 10Last Post: 27-11-2003, 09:05 AM