    R410A leakage



    System -Daikin VRV III,Outdoor model -RXYQ18PY,Indoor model -FXFQ100PVE
    What is the easy way to check the R410 leakage ? Is there is any error code for decrease in pressure? then how to find it.



  2. #2
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    49
    Posts
    6
    Rep Power
    0

    Re: R410A leakage

    Weigh out the charge and compare it to initial charge there is no quick fix!

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: R410A leakage

    Providing that the system comissioning was done correctly i.e autocharge function,full learning curve were carried out the VRVIII can perform a refrigerant containment check then using the binary codes you can work out the amount lost but if the system does have a leak on it you need to carry out recovery setting and pull the gas and pressure test.
    follow this link
    www.extranet.daikin.co.uk
    for the service manuals for this kit it'll tell you how to carry out the above functions
    Si34-601 should be the manual you require

    edit: use http://extranet.daikin.co.uk , but you will need to register on the site.
    Last edited by Brian_UK; 27-04-2010 at 10:41 PM. Reason: Corrected URL, Brian

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: R410A leakage

    You may be able to get some indication from the service code 41, which wil give an indication of the air and coil temperatures. If the system is short of refrigerant there should be a noticeable difference in values when compared to the expected or previously observed. However if the system is only slightly short, the temperature may still be acceptable. Only sure way is to reclaim and weigh the refrigerant as previously suggested.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

Similar Threads

  1. Pipes to large for R410a??
    By Spanglishsparky in forum Technical Speculations
    Replies: 6
    Last Post: 09-05-2009, 12:57 AM
  2. My freezer inner pipe leakage
    By syaful in forum Domestic
    Replies: 3
    Last Post: 05-03-2009, 10:52 AM
  3. Pressure Testing for R410a
    By Pooh in forum Tools and Calculators
    Replies: 33
    Last Post: 13-08-2008, 11:41 PM
  4. R410A pressure in air conditioning
    By irwinchong80 in forum Technical Discussions
    Replies: 4
    Last Post: 06-10-2007, 07:33 PM
  5. R410A captube sizing for 2.5 bar / 35 psi pressure drop
    By DaBit in forum Technical Speculations
    Replies: 10
    Last Post: 27-11-2003, 09:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •