    Bedroom not cool



    Hello everyone

    I face some problem with my bedroom air-conditioning because not cool .Could anybody guide me to solve this problem .Any advice would be appreciate .

    It is National 1 Hp ( 2.55 kw cooling capacity ),R22 .
    Ambient temperature +32°C .The evaporator only have 3 rolls with condensation ,others remain dry .i have checked the pressure at low side,it was 55psi( SST= -1°C ) .Evaporator clean and fan rotate in correct direction .Some time the compressor overload cut out when the body too hot .

    Is it the superheat too high ?
    Is the system less of refrigerant ?
    or the piping has block ?

    your advice would be very appreciated .Thank you.

    Regards
    Oilzee
    Last edited by oilzee; 26-04-2010 at 05:12 PM.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Bedroom not cool

    I'd be removing the refrigerant and weighing it to see if the system is short. If it is short then you'll need to start looking for a leak before doing much more.

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Bedroom not cool

    hi what is your hi side pressure?
    What is the temp in the room your cooling and what is the supply temp?
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Jan 2008
    Location
    lanxi city, zhejiang ,china
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Bedroom not cool

    short the gas ?

  5. #5
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Bedroom not cool

    I would say its a shortage of refrigerant. The fact you only have 3 rows of coils that are wet suggest that there isnt enough gas.

    You will have to call an engineer to find the leak and repair.

  6. #6
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Bedroom not cool

    3 rows of coils wet but none frozen could possibly indicate an issue with the distributor.. are the 3 rows right next to each other or are the 3 rows spread throughout the coil? is it a multifold coil? have you had the cover off and see if all the coil feeder tubes are getting cold?
    -Christopher

  7. #7
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Bedroom not cool

    Quote Originally Posted by monkey spanners View Post
    I'd be removing the refrigerant and weighing it to see if the system is short.
    I would try your suggestion if others solution can't solved it .Thanks

  8. #8
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Bedroom not cool

    Quote Originally Posted by monkey spanners View Post
    I'd be removing the refrigerant and weighing it to see if the system is short. If it is short then you'll need to start looking for a leak before doing much more.
    Quote Originally Posted by goshen View Post
    hi what is your hi side pressure?
    it only have low side service valve . Evaporator air in and air out temperature have not taken yet .Thanks

  9. #9
    Join Date
    Aug 2008
    Location
    malaysia
    Posts
    76
    Rep Power
    16

    Re: Bedroom not cool

    Quote Originally Posted by cadillackid View Post
    3 rows of coils wet but none frozen could possibly indicate an issue with the distributor.. are the 3 rows right next to each other or are the 3 rows spread throughout the coil? is it a multifold coil? have you had the cover off and see if all the coil feeder tubes are getting cold?
    -Christopher
    This is wall type air conditioner . the evaporator coil and pipe line ( 10 feet long ) do not frozen . The cooling coil only wet (3 rolls ) at the middle of the coil .upper and lower coil are dry . Its look like evaporator in a hunger . Thanks
    Last edited by oilzee; 27-04-2010 at 09:11 AM.

  10. #10
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Bedroom not cool

    my vote is for a blockage in the evap coil distributor.. obviously the easiest thing at this point would be to recover and replace by weight the refrigerant.. you could also sdwitch the unit over to heat(reverses flow of refrigerant) then back to cool. if there is a blockage in the distributor it might clear.. (although would likely come right back).
    -Christopher

Similar Threads

  1. Europa Cool or not cool ?
    By UKGENT in forum Transport
    Replies: 2
    Last Post: 18-01-2009, 08:10 PM
  2. Replies: 7
    Last Post: 27-08-2008, 04:58 PM
  3. Cool Pack
    By tjk2007 in forum Tools and Calculators
    Replies: 3
    Last Post: 27-04-2008, 06:59 AM
  4. question on hot gas and cool gas defrosts
    By beachfronttech in forum Supermarket Refrigeration
    Replies: 9
    Last Post: 19-01-2008, 01:50 AM
  5. High cool problem
    By gauge in forum Air Conditioning
    Replies: 2
    Last Post: 04-08-2006, 06:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •