Results 1 to 10 of 10
    Aug 2008
    malaysia
    Bedroom not cool
    Hello everyone
    I face some problem with my bedroom air-conditioning because not cool .Could anybody guide me to solve this problem .Any advice would be appreciate .
    It is National 1 Hp ( 2.55 kw cooling capacity ),R22 .
    Ambient temperature +32°C .The evaporator only have 3 rolls with condensation ,others remain dry .i have checked the pressure at low side,it was 55psi( SST= -1°C ) .Evaporator clean and fan rotate in correct direction .Some time the compressor overload cut out when the body too hot .
    Is it the superheat too high ?
    Is the system less of refrigerant ?
    or the piping has block ?
    your advice would be very appreciated .Thank you.
    Oilzee
    3,853
    Re: Bedroom not cool
    I'd be removing the refrigerant and weighing it to see if the system is short. If it is short then you'll need to start looking for a leak before doing much more.
    Apr 2009
    israel
    778
    hi what is your hi side pressure?
    What is the temp in the room your cooling and what is the supply temp?
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
    Jan 2008
    lanxi city, zhejiang ,china
    14
    short the gas ?
    Oct 2008
    North East
    1,050
    I would say its a shortage of refrigerant. The fact you only have 3 rows of coils that are wet suggest that there isnt enough gas.
    You will have to call an engineer to find the leak and repair.
    Jun 2009
    Columbus Ohio
    55
    169
    15
    3 rows of coils wet but none frozen could possibly indicate an issue with the distributor.. are the 3 rows right next to each other or are the 3 rows spread throughout the coil? is it a multifold coil? have you had the cover off and see if all the coil feeder tubes are getting cold?
    -Christopher
    Aug 2008
    malaysia
    I would try your suggestion if others solution can't solved it .Thanks
    Aug 2008
    malaysia
    Quote Originally Posted by goshen View Post
    it only have low side service valve . Evaporator air in and air out temperature have not taken yet .Thanks
    Aug 2008
    malaysia
    Quote Originally Posted by cadillackid View Post
    -Christopher
    This is wall type air conditioner . the evaporator coil and pipe line ( 10 feet long ) do not frozen . The cooling coil only wet (3 rolls ) at the middle of the coil .upper and lower coil are dry . Its look like evaporator in a hunger . Thanks
    Jun 2009
    Columbus Ohio
    55
    169
    15
    my vote is for a blockage in the evap coil distributor.. obviously the easiest thing at this point would be to recover and replace by weight the refrigerant.. you could also sdwitch the unit over to heat(reverses flow of refrigerant) then back to cool. if there is a blockage in the distributor it might clear.. (although would likely come right back).
    -Christopher
  1. Europa Cool or not cool ?
    By UKGENT in forum Transport
    Last Post: 18-01-2009, 08:10 PM
  2. Replies: 7
    Last Post: 27-08-2008, 04:58 PM
  3. Cool Pack
    By tjk2007 in forum Tools and Calculators
    Last Post: 27-04-2008, 06:59 AM
  4. question on hot gas and cool gas defrosts
    By beachfronttech in forum Supermarket Refrigeration
    Last Post: 19-01-2008, 01:50 AM
  5. High cool problem
    By gauge in forum Air Conditioning
    Last Post: 04-08-2006, 06:54 PM