    heres one for you



    cold store, -22, r404a.

    little comercial / light industrial job.

    has a suction seporator on the system....


    ...heres my problem.


    bringing liquid back to the compressor, now i have checked the fan coils are clear, fans running fine, checked expansion valve super heats, both ok (about 6 degrees) liquid line SV wroking correctly, the system is not over charged either.

    i really do think ive checked everything i can.

    any other suggestions???



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: heres one for you

    If the superheats at the evap outlets are 6K, then it can't have liquid entering the compressor.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: heres one for you

    Quote Originally Posted by murphyboy View Post

    any other suggestions???
    Check suction superheat at compressor suction and measure pipe temperature 25 cm from compressor.
    Use precise and calibrated gauges and thermometer. Zero your gauges for altitude. Isolate temperature probe and pipe at measuring point. Use appropriate probe for job. Wait 2 min or more before temperature reading. Post new readings including:

    Evap air in temp
    Evap air out temp
    Saturated suction temp (convert from pressure)
    Suction line temp at evap outlet
    Suction line temp at compressor inlet

    Cond air in
    Cond air out
    Saturated condensing temp (convert from pressure)
    Liquid line temp at condenser outlet

    Explain do you have any suction/liquid line heat exchangers and at what points you are measuring pressures and how far from temperature measuring points.
    Last edited by nike123; 26-04-2010 at 12:54 AM.

  4. #4
    Join Date
    Aug 2008
    Location
    Auckland
    Age
    55
    Posts
    259
    Rep Power
    21

    Re: heres one for you

    Got a liquid line/Suction line heat exchanger anywhere in the system perchance?

  5. #5
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: heres one for you

    May be leaking liquid / suction heat exchanger inside fan coil unit.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: heres one for you

    Until we see the compressor inlet superheat, we have no evidence that there is a floodback problem.

  7. #7
    Join Date
    Dec 2008
    Location
    manchester
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: heres one for you

    ive taken my pressure from a schrader point i brazed onto the exp equalising line. if i was leaking liquid id expect to be seeing stupid pressures at my suction wouldnt i?

    there is a small slop pot which the liquid line does pass through, but as before if liquid at discharge pressure was leaking into my suction id have daft pressures.

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: heres one for you

    What makes you think the system may have liquid returning to the compressor?

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: heres one for you

    The TX vav is obviously hunting, satuarting suction, equals flood back.

  10. #10
    Join Date
    Dec 2008
    Location
    manchester
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: heres one for you

    ice build up around the compressor windings (bitzer sealed comp), ice cold on suction side of cylinder head, oil sep with frost, oil flushed from compressor sump.


    txv is working fine

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: heres one for you

    Quote Originally Posted by murphyboy View Post
    ice build up around the compressor windings (bitzer sealed comp)
    That doesnt mean liquid in compressor. That only mean that suction line temperature and part of compressor is below 0°C. If room is -22°C than evaporation temp is around -27°C to -30°C.
    You must have than 27K suction superheat to get rid of ice at suction.



    , ice cold on suction side of cylinder head
    Same as above!


    , oil sep with frost,
    oil flushed from compressor sump.
    That is probably related!


    txv is working fine
    Maybe, but 6K superheat at design temperature is litlle to high.

    Why is that hard to take measurements we asked, and post it here, than we could make our own conclusions?

  12. #12
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: heres one for you

    Good points, Nike.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: heres one for you

    I am in the manchester area (today), If you need a second pair of eyes, I can assist, cost you a cub of cha and a bacon butty. PM me if you need help

  14. #14
    ekeller's Avatar
    ekeller Guest

    Re: heres one for you

    if ice on seperater may mean you have very cold vapor at-22degress doesnot mean u have liquid

  15. #15
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: heres one for you

    .

    As others have said.

    Frost on the suction can garentee one thing only.

    The suction is colder than 0 deg C.

    Cool runnings.

    .

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: heres one for you

    The enthalpy of vapour will not form ice on suction, unless satuarated, the degree of saturation is the key.
    So what is the SST at compressor, and what is the superheat?