    Dehumidification System



    Dear Sir,
    At present we are using a AHU with dehumidification from CARYAIRE capacity 9000 CFM.
    The present system contain Desiccant Rotor with two electrical coil of 24 KW each, and our aim is to replace the electrical heating coil with a steam heating coil.
    My question is what is the best and simple way to do it, if we want to do it with our own (including controlling system), and what are the critical points if we want to do it with the help of third party?
    Our expected Humidity range is (RH) 30-60%.



  2. #2
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Dehumidification System

    This should be reasonably easy. However, you first need to be sure of the temperature requirements of the reactivation process. Some are quite high and would require high pressure steam. Others will reactivate quite well using hot water at 90 degrees. Best first step would be to talk to the manufacturer.

  3. #3
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Dehumidification System

    Why do you want to use steam for the reactivation air instead of the simple electrical coil?. The process and properties of steam is complicated. To get the required temperature and mass flowrate you have to control the outlet pressure and study the steam saturation properties before it becomes steam condensate. You also need a steam generating unit, and think about its fuel and maintenance costs.

  4. #4
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Dehumidification System

    Thanks, now i need clarification.......
    Actually its a pharma industry and we have a prity good gas fired boiler, and we also provide a steam line for the AHU unit, we just need to install a system.
    48 kw 12 hrs and 25 days in a month, electric bill is quite high. In Bangladesh power is not available, and we need to pay a fixed amount for gas, we r paying the gas bill but utilization is low, so to optimize the situation we r looking for steam coil dehumidification!

  5. #5
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Dehumidification System

    Now i got your point. Redesigning into steam coil heating is a good alternative heat source due to the present conditions you've mentioned. As chalie_n said, you must first consult the "OEM" of the dessicant rotor and discuss your ideas as well as ask the critical points to look for (e.g. desiccant air correct temp.,etc.). As for the steam piping, I'm sure you already have ideas because you have your own steam system. The usual piping accesories like isolating valves, PRV, relief valve, steam trap, solenoid valve, gauges, etc. should be included.

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Dehumidification System

    hi bashir, just a point of interest , is the system full recycle , or how much fresh air intake have you got?

  7. #7
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Dehumidification System

    We take near about 10 to 20 % fresh air in the cycle, and obviously we exhaust some portion of the return air.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Ammonia Heat Pumps
    By US Iceman in forum New Technologies
    Replies: 39
    Last Post: 22-03-2010, 06:36 PM
  3. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 03:18 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •