    R407c top up.



    Hello all, I would like to find out two things, first is it possible to "top up" an R407c system in liquid form due to the refrigerant being a mixture of three different gases?

    The second question is linked to the above question, would an unbalanced R407c system cause a heat exchanger on the condensor side of a printing press chilling unit to burst? It is running two ZR11 M3 scrolls in parrallel?

    Regards,

    Shannon.



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: R407c top up.

    When R407C leaks, you can end up with a "refrigrant mix" with operating pressures similar to R410A. It is not practical to determine the remaining refrigerant and is usually best to reclaim and start again with new refrigerant. As to the bursting problem, that could be due to the previously mentioned high pressures or may be somethingn unrelated.
    Check the rating plate on the heat exchanger and compare with R410A head pressures, which could easily be up to possibly 450-500 psig. Pesumably the heat exchanger has water as one of the medium, check the circulation pumps or pipework for a partial blockage. Make sure that you have identified and rectified the cause before fitting a new heat exchanger, or the same problem could re-occur.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

  4. #4
    Join Date
    Nov 2009
    Location
    Poland
    Posts
    82
    Rep Power
    15

    Re: R407c top up.

    R407C gas loss supplements are not due to the fact that you do not know what will fill the component and the reason is that this is a dissection in the gas cylinder.
    Please remove the old fill factor and re-checking system overheating and evaporation.

Similar Threads

  1. r407c
    By dunny123 in forum Supermarket Refrigeration
    Replies: 6
    Last Post: 28-04-2010, 07:30 AM
  2. Loss of R407c performance at high temperature
    By SETCURE in forum Refrigerants
    Replies: 2
    Last Post: 06-08-2009, 05:39 PM
  3. r407c chiller issue
    By Lc_shi in forum New Technologies
    Replies: 3
    Last Post: 09-01-2008, 01:22 AM
  4. R407C to R404a
    By MaDiNfO in forum Air Conditioning
    Replies: 10
    Last Post: 30-07-2006, 09:34 AM
  5. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •