06-07-2005, 08:45 PM #51
Re: refrigerant velocity in evaporator
Hi Peter,
There is adifferent angle to the oil problem. For proper oil seperation there should be sufficient discharge super heat.Ex in case of R22 more than 25 deg F.Say your compressor runs with liquid flood back or sucking wet vapour you normally end up with oil problems
-
06-07-2005, 09:38 PM #52
Re: refrigerant velocity in evaporator
Originally Posted by patrickj
Hi...I think this thread is about a reciprocating unit where it would be the suction superheat that is important to stop refrigerant flooding to the compressor......the discharge superheat as applicable to oil seperation is normally when there are mesh seperators on the discharge side of screw compressors.Best regards etc
-
09-07-2005, 12:37 PM #53
Re: refrigerant velocity in evaporator
Originally Posted by BESC5240
-
11-07-2005, 08:12 AM #54
Re: refrigerant velocity in evaporator
Originally Posted by Gary
No it isn't.
The condensing unit is mounted under the the evaporator.
-
11-07-2005, 12:11 PM #55
Re: refrigerant velocity in evaporator
Seems to me that it would work much better if the flow were reversed. Each path would be downhill all the way, instead of uphill. Velocity is only important where refrigerant vapor is trying to push oil uphill.
Last edited by Gary; 12-07-2005 at 12:01 PM.
Similar Threads
-
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
low velocity on evaporator fans ?!?!
By cruzeiros in forum Technical DiscussionsReplies: 22Last Post: 10-12-2008, 05:00 PM -
Air Source Heat Pump - temp of refrigerant leaving evaporator
By anup in forum FundamentalsReplies: 3Last Post: 06-11-2006, 05:04 AM -
Which refrigerant to use for low temp apps?
By DaBit in forum Technical SpeculationsReplies: 14Last Post: 21-09-2002, 03:17 PM