    Re: refrigerant velocity in evaporator



    Hi Peter,
    There is adifferent angle to the oil problem. For proper oil seperation there should be sufficient discharge super heat.Ex in case of R22 more than 25 deg F.Say your compressor runs with liquid flood back or sucking wet vapour you normally end up with oil problems



  2. #52
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Smile Re: refrigerant velocity in evaporator

    Quote Originally Posted by patrickj
    Hi Peter,
    There is adifferent angle to the oil problem. For proper oil seperation there should be sufficient discharge super heat.Ex in case of R22 more than 25 deg F.Say your compressor runs with liquid flood back or sucking wet vapour you normally end up with oil problems

    Hi...I think this thread is about a reciprocating unit where it would be the suction superheat that is important to stop refrigerant flooding to the compressor......the discharge superheat as applicable to oil seperation is normally when there are mesh seperators on the discharge side of screw compressors.Best regards etc

  3. #53
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: refrigerant velocity in evaporator

    Quote Originally Posted by BESC5240
    Comming back to my original question. In attachment you will find a picture of the evaporator.
    It consists of 2 coils. One coil for the refrigerant (R134a) and the second one for the fluidum to be cooled.
    The refrigerant goes through the distributor, through the distibutor lines (which to me are not optimally positioned), and than the refrigerant does in to a 5/8" (smooth) horzontal tube. The length is 6 m. In the middle of the coil (at the end of the tube) the tube goes up to a next level, and in to a 2nd layer of a 6 m 5/8" tube. This 2nd level tube also stays horizontal and goes from the inside to the outside of the coil.
    Comming outside it goes into a header.
    So you have 18 layers of a 6 m tube, and 9 circuits. In the middle of each circuit you have a difference in height of 16 mm (5/8").
    This evaporator is put into a glycol solution and the compressor is controlled by a thermostat in the glycol.
    I have calculated the velocity of the gas comming out of each circuit : 0,65 to 0,8 m/s depending on the conditions and the type of compressor used on the evaporator.
    I compare this to the values that i can calculate on 'standard' heat exchangers (like shell and tube heatexchangers from Heatcraft) : I get values between 2,8 and 6 m/s. Can any one confirm these values?
    Is the evaporator in the picture upside down?

  4. #54
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: refrigerant velocity in evaporator

    Quote Originally Posted by Gary
    Is the evaporator in the picture upside down?
    Dear Gary,
    No it isn't.
    The condensing unit is mounted under the the evaporator.

  5. #55
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: refrigerant velocity in evaporator

    Seems to me that it would work much better if the flow were reversed. Each path would be downhill all the way, instead of uphill. Velocity is only important where refrigerant vapor is trying to push oil uphill.
    Last edited by Gary; 12-07-2005 at 12:01 PM.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. low velocity on evaporator fans ?!?!
    By cruzeiros in forum Technical Discussions
    Replies: 22
    Last Post: 10-12-2008, 05:00 PM
  3. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  4. Which refrigerant to use for low temp apps?
    By DaBit in forum Technical Speculations
    Replies: 14
    Last Post: 21-09-2002, 03:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •