    hi guy's

    we've been asked to quote to replace some old kit in a path lab in a big hospital. However it's on R22 and they want it to be on some of that fancy new cold stuff like 404a

    the pipe run is about 60 m and the install quality is such that it seems a real pity to rip it out..

    now then is there anything around which would flush the pipes to a sufficient standard??

    (and no we can't fit a mitsi wall mount!!)

    cheers

    richard



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: cleaning old pipework

    Hi Richard,

    I have posted in the past about some special solvent for this purpose.

    But Every refrigerant supplier, will have their oun.

    Chemi

  3. #3
    Join Date
    Mar 2004
    Location
    UK
    Posts
    625
    Rep Power
    21

    Re: cleaning old pipework

    Hi

    I,ve used endo-flush from nrs on several occasion and alls worked well

    cheers b

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: cleaning old pipework

    how long does it take to flush the pipes out and do you need anything else to do it with -pumps etc??

    cheers

    richard

  5. #5
    Join Date
    May 2004
    Location
    southern england
    Age
    69
    Posts
    86
    Rep Power
    20

    Re: cleaning old pipework

    Change the oil to POE and run with R22 until below 5% mineral content. Then change the unit and expansion device to R404a. A wise move would be to fit a drier shell in the suction as the R404a will scour the crap off the inside of the pipes and return it to the compressor ( unless pipework was installed with purged Ofn)??.
    it's only a fridge, fix it. ;)

  6. #6
    rbartlett's Avatar
    rbartlett Guest

    Re: cleaning old pipework

    Quote Originally Posted by chillyhamster
    Change the oil to POE and run with R22 until below 5% mineral content. Then change the unit and expansion device to R404a. A wise move would be to fit a drier shell in the suction as the R404a will scour the crap off the inside of the pipes and return it to the compressor ( unless pipework was installed with purged Ofn)??.

    the problem here is that the old stuff is shafted and doesn't work..

    cheers

    richard

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: cleaning old pipework

    the problem here is that the old stuff is shafted and doesn't work..
    You can always use a recovery machine to cycle the flushing liquid through the pipework. Just make sure it's an oilless compressor.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: cleaning old pipework

    You can always use OFN to push it, just put some thing at the other end to collect it.

    Chemi

  9. #9
    Join Date
    Mar 2004
    Location
    UK
    Posts
    625
    Rep Power
    21

    Re: cleaning old pipework

    Hi Richard Pump the endo flush through with oil pump until it comes out other end,then send ofn through to blow remainder out,always measure amount in and out as this stuff won,t evaporate,repeat until your happy with the colour,Your aiming to get 95 % out of what you put in.All the instruction are on the bottle.

    cheers ber

  10. #10
    Join Date
    Apr 2005
    Location
    Moscow
    Age
    48
    Posts
    20
    Rep Power
    0

    Re: cleaning old pipework

    Hi
    You can use R-11 (or other refrigerant which doesn`t evaporate at atmosphere pressure) to clean up the system & remove old oil from the system, especially from evaporator & condenser.

    SNi

  11. #11
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    601
    Rep Power
    28

    Re: cleaning old pipework

    Not in this country, pal! ;-) R11 is illegal here. Richard, I'm told that we've used Endoflush before with good results, but that getting it all out was a challenge. MInd you, we were cleaning the whole system, comp. included!

  12. #12
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: cleaning old pipework

    Hey' Hey, Hey

    You do not say here R-11, R-12 and R-502 unless it is in the past tense.

    I have used yesterday AXAREL 6100, 1 to 1 replacement of good old R-11.
    Did remarkable job, had to heat the coil a bit while vacuum was on.
    http://www.techchem.net/solventcleaners.htm

    About the "pleasent" odor, my a**s.

    Chemi

  13. #13
    rbartlett's Avatar
    rbartlett Guest

    Re: cleaning old pipework

    Quote Originally Posted by SNi
    Hi
    You can use R-11 (or other refrigerant which doesn`t evaporate at atmosphere pressure) to clean up the system & remove old oil from the system, especially from evaporator & condenser.

    SNi
    Sni

    Sadly r11 was banned in the UK years ago... and the flushing using refrigerant is considered wrong too..

    cheers

    richard

  14. #14
    shuki's Avatar
    shuki Guest

    Re: cleaning old pipework

    does anyone know where i can get R141b, this is much better than Endoflush as its easy to get it out

  15. #15
    TWINCHRISHANNAH's Avatar
    TWINCHRISHANNAH Guest

    Re: cleaning old pipework

    Why flush the system, You can use iceon 59 as a direct replacement for the r22 withoutchanging oil!!!

    bit quicker

  16. #16
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: cleaning old pipework

    Quote Originally Posted by TWINCHRISHANNAH View Post
    Why flush the system, You can use iceon 59 as a direct replacement for the r22 withoutchanging oil!!!

    bit quicker
    You need to re-read the original post and subsequent ones, from the originator, in the thread to answer your own question.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  17. #17
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Thumbs up Re: cleaning old pipework

    Quote Originally Posted by rbartlett View Post
    hi guy's

    we've been asked to quote to replace some old kit in a path lab in a big hospital. However it's on R22 and they want it to be on some of that fancy new cold stuff like 404a

    the pipe run is about 60 m and the install quality is such that it seems a real pity to rip it out..

    now then is there anything around which would flush the pipes to a sufficient standard??

    (and no we can't fit a mitsi wall mount!!)

    cheers

    richard
    Richard
    Your thread is a little old now. But if the link below is
    no longer needed. Someone else may benifit.
    Once on the webpage scroll down to the bottom and read about Isceon's replacement for R141b.
    Available as a complete kit for cleaning systems.
    I assume this will also be available in U.S.A. as they are part of Dupont I think?
    That's if you guys (from across the pond)have the same restrictions as us?
    Grizzly

    http://www.idsrefrigeration.co.uk/in...ntent=cleaning

  18. #18
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: cleaning old pipework

    Yes Grizzly, we do have the same restrictions and as I understand it 141b is now out. I was just looking for some alternatives, on the net, to the highly expensive products sold here in France and came across this:
    http://www.nucalgon.com/nucalgon/nuc...1?OpenDocument

  19. #19
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: cleaning old pipework

    Having only just clicked the link you put up I will add that I coincidently have my catalogue open at the FRIOPACK page and it retails at:

    Nettogaz GC1 Friopack 13kg 1,365 euros
    Nettogaz Greenclean Friopack 10kg 516 euros



    "Sorry mate looks like the compressor's burnt out. Here's your quote":

    300 euros comp

    150 euros labour (inc brazing + vac out)

    1,365 euros for the internal flushing agent (don't worry about the labour on that part, you've suffered enough)

Similar Threads

  1. Pipework Flushing
    By frank in forum Air Conditioning
    Replies: 9
    Last Post: 22-08-2009, 07:15 PM
  2. Never ending cleaning condensor
    By Drefer in forum Industrial
    Replies: 10
    Last Post: 24-04-2006, 02:53 PM
  3. Pipework cleaning up (Inside)
    By Latte in forum Air Conditioning
    Replies: 6
    Last Post: 22-10-2005, 05:55 PM
  4. Porus pipework
    By Latte in forum Supermarket Refrigeration
    Replies: 17
    Last Post: 05-04-2005, 11:55 PM
  5. Cleaning suction strainers.
    By Stuart Ginbey in forum Air Conditioning
    Replies: 6
    Last Post: 26-05-2004, 02:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •