    help!thermosyphon oil cooling



    help!thermosyphon oil cooling
    Now I am designing a propane thermosyphon oil cooling,but I don't know how to caculate the liquid line Diameter from the receiver tho the heat exchanger.According with the IR hand book.the pressure gradient for this pipe are 22.6pa/m for R22.What's the means of pressure gradient?and how to caculate the Diameter by the pressure gradient.



  2. #2
    Join Date
    Aug 2008
    Location
    California
    Posts
    28
    Rep Power
    0

    Re: help!thermosyphon oil cooling

    The pressure gradient is the pressure drop per unit of length of pipe.

    The first step is to calculate the required flow rate required by your oil cooling requirement. Times your recirculation rate.

    Next step is to find the viscosity valves of your refrigerant.

    Next is to calculate the “head loss” of this flow rate though various pipe sizes. Choose the pipe size that has less than or equal to your desired pressure gradient.

Similar Threads

  1. help!thermosyphon oil cooling
    By joanna in forum System Optimization
    Replies: 2
    Last Post: 28-04-2010, 04:52 AM
  2. Cooling problem with VRV REYQ24M7.
    By cool#9 in forum Air Conditioning
    Replies: 3
    Last Post: 07-02-2010, 12:20 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •