    daikin rsey8



    The saga continues, had an e9 error(faulty eev or outdoor board), both exp. valves meter out ok so i replaced the outdoor board.

    How long does self address take? I pressed reset for 5 seconds as per manual, unit not showing on dbacs after 1 hour, should i be worried?

    alec



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: daikin rsey8

    Try powering down the master unit keep reset pushed in and power back up re address should about 15 mins this works on reyq vrv3

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: daikin rsey8

    Thanks james, i'll give it a go, only worry is that e9 is still up on indoors.

    Alec

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: daikin rsey8

    once you've powered down the outdoor unit the fault codes should dissapear
    if all else fails contact Daikin Technical 01932879200

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: daikin rsey8

    Ok, powered down indoors and outdoor, repowered indoors and reset outdoor.

    Outdoor not registering on dbacs and indoors faulting on E9 again

    Any ideas? Could the expansion valve board be faulty?

    Thanks for the input so far....

    alec

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: daikin rsey8

    are the dip switches the same as the old pcb? not sure on the expansion valve if you have another unit the same on site it might be worth comparing the resistance of the motors and outputs from the pcb
    Last edited by james10; 20-04-2010 at 08:17 PM.

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: daikin rsey8

    James

    No dips on this board or the old one, weird that its dropped off the dbacs.

    Alec

  8. #8
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: daikin rsey8

    Alex
    i've been reading upon your E9 error code and found an alternative description to the daikin text description this description points directly to the expansion valve coil

  9. #9
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: daikin rsey8

    Thanks james, i'll order up two valves and the expansion valve board, could be a bit of trial and error....

    Thanks for the help

    alec

  10. #10
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: daikin rsey8

    How did you get on with the valves?

  11. #11
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: daikin rsey8

    Hi James

    Believe it or not i'm still waiting on the valves and the go ahead from the customer, speaking to a previous tech who serviced these units this has happened before with the same symptoms so i'm confident that the valves will fix the problem. Thanks for the help

    alec

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Panasonic Urban rebadged Daikin
    By complete HVAC in forum Air Conditioning
    Replies: 0
    Last Post: 19-08-2009, 04:35 PM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •