    Pump Down cycle with EPR



    Hi,

    I've been servicing a couple of 4' open display merchandisers - each individually served by a dedicated condensing unit.

    The system employs an evaporator pressure regulator and cycles on pump down via liquid solenoid valve.

    I am concerned about proper pump-down control setting. The EPR is set at a minimum 18degF evaporator temperature (R-22). At times, when the EPR modulates, the suction pressure back to the compressor can drop to 15 to 20 psi so the cut-out is needed to be set lower than such occurance.

    On pump-down (cut-out set at 5 to 10 psi) and cycle off, the suction pressure will rise to the 18degF SST pressure plus the superheat setting of the expansion valve (approx. 45 psi). Some short-cycling is evident during off-cycle, and obtaining satisfactory shut-down of the condensing unit under the cool ambient conditions that now exist is somewhat tedious.

    I slept on it last night, and considered perhaps more satisfactory results would be obtained with use of a suction stop solenoid valve, as opposed to the liquid line solenoid valve in conjunction with the application of the EPR.

    Any thoughts or observations?



  2. #2
    Join Date
    Jan 2002
    Location
    Long Beach Ca
    Age
    48
    Posts
    47
    Rep Power
    0

    Re: Pump Down cycle with EPR

    how excessive is the short cycling?

  3. #3
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Pump Down cycle with EPR

    To my reasoning shutting the suction in preference to the liquid line may allow refrigerant to migrate or condense in the evaporator on the off cycle. This may give you an additional problem with liquid return when the compressor starts up. Added to this is the oil carry over on short cycles ? you may end up with most of your oil stranded around the system until it gets enough legitimate run time to pull it back.

    If the temperature gradient in the cabinet is stable during this off-cycle, why not consider a timer relay providing a minimum off-time after pump down. As a solution it is relatively inexpensive and does not involve costly surgery to the refrigeration circuit. You can get them with adjustable time periods so that you can determine the optimum time period yourself.

    Hope this helps
    ________
    CT70
    Last edited by Argus; 07-02-2011 at 08:17 AM.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pump Down cycle with EPR

    In all freezers that I build, a EPR is present and I never had a problem.
    To my opinion, it never closes completely so pump down should work.

    If you encounter a real problem with pump down, you can increase superheat and set the EPR to a lower temp.

    Chemi

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Pump Down cycle with EPR

    I've been servicing a couple of 4' open display merchandisers - each individually served by a dedicated condensing unit.
    Hi Mark

    If the units are served by individual condensing units, why do you need EPR's?

    Why not convert the cabinets to control the pump down on stats?

  6. #6
    Join Date
    May 2004
    Location
    southern england
    Age
    69
    Posts
    86
    Rep Power
    20

    Re: Pump Down cycle with EPR

    If they are low temp cases, are they EPR's. Presume the units have electric defrost. Are the Tev's Mop or N. If the TEV's are not Mop then the units should have crankcase pressure regulators to stop compressor starting under high crankcase conditions.
    it's only a fridge, fix it. ;)

  7. #7
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23

    Re: Pump Down cycle with EPR

    Hi. The sytem installation application is specified by Masterbilt to include the EPR's. I talked directly to the factory. The units are a commercial temperature application - open dairy case, and do employ electric defrost.

    I am able to set the low pressure control to limit any short-cylcling to something NOT TOO disconcerting.

    One other thing that has always bugged me on these systems, is that the EPR is mounted exactly at the suction inlet to the condensing unit, with upt 60' of lineset between the control and the evaporator (case). Typically, this results in Johnny the trunk-slammer to mistaken the control for a "C"PR (crankcase pressure regulator) and after a period that I have been absent from primary service provider on these units (1-1/2 years or so), I find myself running about resetting the controls. I know what goes through the technician's mind, when the valve is being adjusted, and it has no affect on crankcase pressure (I've been there), but I got down to actually reading the information on the valve on the first visit (8years ago).

    Perhaps if the valve was not so close-coupled with the condensing unit, the affect (that I describe) would not be so pronounced.

  8. #8
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23

    Re: Pump Down cycle with EPR

    Quote Originally Posted by frank
    Hi Mark

    If the units are served by individual condensing units, why do you need EPR's?

    Why not convert the cabinets to control the pump down on stats?

    I hear you. That was my comment to the factory, when I first called them. Perhaps you are right, and the plant misunderstood the application. Perhaps I should call again to verify. It has been many years since I had that conversation.

    I beleive that when the ambient is high (90degF to 110degF) in my part of the world, the high temperatures/pressures eliminate the operating conditions that I am observing now, in 60degF or so ambients, performing major service on the cases.

    Regards.

  9. #9
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Pump Down cycle with EPR

    A few years ago I was working on an old belt driven comp which was leaking back accross the head causing it to short cycle but the customer would not buy a new one. So I rewired it to stop it short cycling, if i remember how I done it ill post it but im sure it can be done.
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Pump Down cycle with EPR

    You could of course increase the differential on the LP to make the "cut in" greater than 45psig, say 55psig. As the units are on R22 the standing pressures should be in excess of this at switch on.

  11. #11
    Join Date
    Jul 2001
    Location
    Northern New York
    Age
    62
    Posts
    42
    Rep Power
    0

    Re: Pump Down cycle with EPR

    I think Frank hit the nail on the head. If the units are sized right, why are there EPR valves? They would only serve to reduce efficiency and cause pumpdown issues. I would simply remove them or cycle the unit on the temp control and eliminate the pumpdown entirely. Was this unit put together at the factory or in the field? Masterbilt may have made it for use with a rack.
    Last edited by terrygoodrich; 17-03-2005 at 03:37 AM.

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pump Down cycle with EPR

    Why not connect the low pressure control to the evaporator side of the EPR?

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pump Down cycle with EPR

    Hi Gary,

    Wouldn't it might be dangerous for the compressor?

    If the EPR will close when the pressure drops, the compressor will work for too long without cooling and might burn.

    Chemi

  14. #14
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Pump Down cycle with EPR

    can you alter the wiring this way?

    live feed through a nc timer to lp switch then comp contactor.
    live feed through defrost timer, stat to s/valve
    from the other contact on the stat conect this to the coil on the timer

    run the system and time how long it takes to pump down then add a few secs and set the timer to this

    now hopefully when the stat shuts down the valve it then counts the timer down then cuts the feed to the lp switch
    when stat calls for cooling it lets the timer close and feeds the lp ( and also feeds the s/valve from the stat)
    Last edited by chillin out; 18-03-2005 at 10:12 PM. Reason: stuffed it up
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. pump down for reverse cycle systems
    By abbasi in forum Fundamentals
    Replies: 4
    Last Post: 21-04-2006, 06:03 AM
  4. New pump
    By Peter_1 in forum Air Conditioning
    Replies: 1
    Last Post: 13-12-2003, 06:19 PM
  5. System Pump Down
    By Brian_UK in forum Technical Speculations
    Replies: 16
    Last Post: 25-10-2001, 10:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •