    on what to save electricity at low-temperature chamber 40000 square meters



    Hi guys help with whatever they can? customer set a target for the design of low-temperature chamber for Maxim with saving electric energy, I designed the electronic gate and inverter compressor, wanted to design a floor heating in the chamber with the heated glycol condensing unit but could not because the car in winter will not give such a load, like to hear what else you can do for energy savings</SPAN>



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: on what to save electricity at low-temperature chamber 40000 square meters

    You Can save on defrost intervals and duration if the RH in the chamber is low.

    You can save a lot if the walls are thick enough.
    Floor should be insulated with polyurethane as thick as the walls so you do not need floor heating.

    When you reach the set point, cut off half of the evaporators fans.

    Make a refrigerated corridor to the main door to avoid warm humid air from entering.

    Im sure other members wll add more ideas.

  3. #3
    andrew1977's Avatar
    andrew1977 Guest

    Re: on what to save electricity at low-temperature chamber 40000 square meters

    Thanks chemi-cool if you can me more about sex

  4. #4
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: on what to save electricity at low-temperature chamber 40000 square meters

    The refrigeration system will easily make enough heat for freeze protection under floor heating. you can also have plenty of heat for the heated areas of the building during the autumn and spring and part of the heating load in winter. This will work if you abandon traditional Russian design practices and build a modern carefully designed building.

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    55
    Posts
    16
    Rep Power
    0

    Re: on what to save electricity at low-temperature chamber 40000 square meters

    Sub cool the liquid.

    On one freezer we cycled all of the evaporator fans off with the thermstat and reduced energy consumption by 40%.

  6. #6
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: on what to save electricity at low-temperature chamber 40000 square meters

    What is the temperature of the of the chamber.
    Prerequisite is to have all walls and ceiling and floor need to be insulated and if it is sub zero temperature you should have vapor barrier treatment prior to insulation. The pull down load can be spread over for longer period for reducing the energy.

    For such a large Cold chamber I would reccommend Brine chiller with indoor evaporator units with brine cooling coil so that moment temperature of room is achieved by having 2 way valve in the indoor cooler cooling coil substantial saving of power by way chiller modulation can be achieved.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. NVQ 3 online test
    By Burrah Boy in forum Training
    Replies: 7
    Last Post: 28-10-2009, 08:35 PM
  4. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •