    Question Sofstarter for Compressor Motor ?



    Dear All,

    I have a question.
    Can I use a softstarter for compressor motor?
    The chiller model is Carrier 30GB-060 (piston compressor)

    Thank you.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Sofstarter for Compressor Motor ?

    Yes you can.

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Sofstarter for Compressor Motor ?

    Yes , piston compressors usually are installed with unloading valves .this results in adverse power ratio because power saving is not linear .
    Hence piston compressors when installed with frequency drive can contribute to the saving of 2o% power . However check the max & minimum speed recommended by compressor manufacturer .

    Also must be careful on high temp application where compressor is selected for say 5 deg c as evap temp may not be permitted to operate at say 59 hz . As the compressor motor might exceed the max rated current. With due care in design & selection ,the frequency drive can be an asset

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Sofstarter for Compressor Motor ?

    Instead of soft starter , use vfd & lock it at say 28 hz for start up frequency for say three minutes & then ramp up the speed of motor speed . Accordingly , use of frequency drive can serve the purpose of soft starter as well as power saver .