    Hot gas bypass



    Hi all hope everyone is well. Just after a bit of advise about a hot gas solenoid valve making a noisey hammering sort of sound. I was called out to a airedale chiller working as part of a close control system . I was called out because chiller wasnt working. Found that the system had lost its gas due to a crack on the hotgas bypass pipework. I cutout the solenoid valve and repaired the leak. I then replaced the solenoid valve. The system now works fine except that the solenoid valve makes a loud hammering sound when the coil energises. I thought it may be the valve which was faulty so I replaced it again but it still makes the same sound. I then thought the solenoid valve was installed the wrong way round but direction wise the flow goes from the discharge to the suction which as far as i know is right. What am I missing is there any other factors governing the installation of the valve
    Last edited by Kirky; 18-11-2010 at 07:56 PM.



  2. #2
    Join Date
    May 2010
    Location
    U.S.
    Age
    68
    Posts
    18
    Rep Power
    0

    Re: Hot gas bypass

    Did you replace it with an OEM solenoid? Is the pressure rating correct?

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Hot gas bypass

    Solenoid valves are not suitable for hot gas bypass(80-90°C). They are only suitable for low temperature liquid refrigerant (40-50°C).
    Additionally, the membrane is subject to pulsation from the compressor, and that's the reason why the pipe broke in first instance.
    It's just a matter of time before it breaks again. It's an inherently design fault from airedale.

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Hot gas bypass

    Hi there,

    I have seen few systems with HGB with solenoid valve. They work OK but when SV opens then you hear gas flow and thus a noise. The same thing happens with HGB valve which regulates the hot gas flow. If you hear "fssssss" then it's gas flow.
    Important thing about HGB is the thermal stress which breaks the joints. The "T" section where the HG is introduced into the suction is the weakest part. A special "T" joint must be used. Danfoss has it.
    In one system I build the "T" joint by two pipes going into each other. Have a look at Danfoss HGB valve cat. the T joint is shown there.

    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. Hot Gas Bypass Valve
    By NewEngineer23 in forum Fundamentals
    Replies: 1
    Last Post: 09-08-2010, 10:43 AM
  2. Pilot operated bypass
    By Aragon in forum Technical Discussions
    Replies: 0
    Last Post: 08-06-2010, 11:27 AM
  3. Chilled water bypass problem
    By MACT in forum Trouble Shooting
    Replies: 5
    Last Post: 16-10-2008, 02:01 AM
  4. old system with hot gas bypass. help!
    By joapysoe in forum Trouble Shooting
    Replies: 8
    Last Post: 20-01-2008, 11:58 PM
  5. Hot gas bypass control?
    By Jase in forum Air Conditioning
    Replies: 9
    Last Post: 29-10-2006, 11:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •