17-04-2010, 01:06 PM #1
single phase compressor wiring
hi guys with old p/cold and c/land compressors the live wire goes on run and start windinds and neutral on common pin ,But on aspera and other can compressors it has neutral on run and start windings and live run on common pin , is there a reason for it ,
-
17-04-2010, 01:39 PM #2
Re: single phase compressor wiring
No. There is no reason and it doesn't make any difference.
Its alternate currant. On a DC it would make a different.
-
17-04-2010, 07:01 PM #3
Re: single phase compressor wiring
Thankyou for info chemi cool.
-
29-04-2010, 05:47 PM #4
Re: single phase compressor wiring
On the old prestcold stuff the live in goes to the compressor terminal box first and then to the box with the relay and caps in so if klixon is in the live circuit and opens, all the power is cut and compressor stops running.
On the aspera and l'unite style comps power goes to the relay box first then to the compressor, so if in this case the klixon was in the live as per prestcold, when it operates the comp would still try to run but only on the start winding... but by putting the klixon in the neutral is breaks the circuit totally.
Jon
Similar Threads
-
single phase 208v
By j.a.violante in forum Air ConditioningReplies: 2Last Post: 24-05-2009, 07:18 AM -
generic single phase contactor?
By paul_h in forum ElectricalReplies: 9Last Post: 06-02-2009, 08:28 AM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
Variable speed drives for single phase motors
By PRESS in forum Air ConditioningReplies: 10Last Post: 10-12-2007, 07:23 PM -
Single phase contactor
By Andy T in forum CommercialReplies: 9Last Post: 23-10-2006, 01:45 PM