    No earth on interconnect- u4



    Re-installed a Daikin inverter multi 80 which has 4 units on the system. As the system was re-installed in the same site pipework and cables re-joined and one unit goes straight into fault u4. Swapped the signal cable with another system momentarily so the system is cross wired. Fault moved onto other ducted unit. Found after eliminating boards etc the earth has a break in it somewhere on that particular interconnect. As the junction box where it was joined is tucked away in a finished ceiling and I cant run a new earth could I tap the earth from a ducted system that is nearby? Does this missing earth cause the u-4 and how exactly? replies much appreciated



  2. #2
    Join Date
    Jan 2009
    Location
    Australia
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: No earth on interconnect- u4

    Hi Jimbo1979, I don't think the broken Earth would cause a U4 Fault, By swapping Interconnects with another unit, like you have and the fault moves to the other unit, shows that it seems to be something wrong with the outdoor unit, I would suggest a new outdoor PCB would be a good start. However the broken Earth issue still exists, and there would be no problem taking an earth from another indoor unit on the same system as you suggested, I would not take an Earth off another separate system, however you could take a separate earth from a switchboard.
    HOPE THIS HELPS

    PS. I had this similar problem recently and a new Outdoor PCB fixed the problem, Remember to put fresh heat paste on the back of the components of the Inverter board. Very Important.

  3. #3
    jimbo1979's Avatar
    jimbo1979 Guest

    Re: No earth on interconnect- u4

    Thanks for the reply Andrew. The client says there is history of outdoor board replacement due to salt because it's near water. Will have to check other boards as we swapped the inverter board on the other identical unit and no joy. Heat paste essential I know as I moved a condenser that was in virtually a cupboard that had a inverter replaced and looks as if they just chucked the new one in and weather got hot and killed it. Will post the outcome. Cant remember first two letters on the model number. Its the old daikin 80 multi inverter. Any ideas anyone?

  4. #4
    Join Date
    Jan 2009
    Location
    Australia
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: No earth on interconnect- u4

    Jimbo,

    Is it a 4MX80, I think that is the old one.

Similar Threads

  1. No earth
    By Andy AC in forum Electrical
    Replies: 8
    Last Post: 14-10-2009, 12:55 AM
  2. Earth leakage/resistance question
    By steemy in forum Electrical
    Replies: 12
    Last Post: 04-08-2009, 10:24 AM
  3. live condenser without earth
    By casino in forum Air Conditioning
    Replies: 7
    Last Post: 21-09-2008, 08:34 PM
  4. Copeland Scrolls going to earth
    By Latte in forum Trouble Shooting
    Replies: 7
    Last Post: 19-08-2008, 09:08 PM
  5. Earth faults
    By reggie in forum Technical Speculations
    Replies: 17
    Last Post: 28-01-2006, 06:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •