Results 1 to 15 of 15
    Mar 2010
    64
    7
    Smile lowering micron readings
    Hi Was thinking of purchasing 3/8" vacuum hoses . I was told this would speed up evacuation and get me a lower micron reading. But the hoses will still attache to 1/4" schrader valves with 3/16" openings. Mostly work on split systems and 10 ton or less roof top units. Wonder what you guys think. Thank you
    Randy
    Feb 2010
    242
    Re: lowering micron readings
    Quote Originally Posted by Randykissling View Post
    Randy
    3/8 shared to your gauge manifold will increase the speed of the vac, slightly.
    But speed is not always best. Depth of vac or a good tripple vac is better than a fast evacuation.
    cool runnings
    Mar 2010
    64
    7
    thanx but will I get a lower micron reading with the larger hoses?
    Jun 2009
    North East England
    41
    712
    My tutor at college had an old manual that said an increase in hose diameter decreases the evacuation time also that every time you double the length of the hose you double the evacuation time. As regards to lowering the micron reading hose daiameter is irrelavant as time and a good vac pump are the only factors in this also as Cool Runnings said triple vac is the best way of getting a good vacuum
    Feb 2010
    242
    No..
    You will only get a lower Micron reading if the vac pump can pull that low (and as long as the system is gas tight).
    No mater what size pipe you vac with you will pull a low vacuum, but the pipe will affect the speed so if you want to vac a system in a few mins you need a hugh vac pump and hugh pipes!! If you have hours to vac out you will always achieve the same level, only time will vary!!
    A tripple vac is the way to go..
    cool runnings.
    Mar 2010
    64
    7
    Thank you guys you have saved me a few bucks
    Oct 2008
    mallorca, spain,
    75
    768
    hi , just read your coments , I allways understud the vacing situation as=2 shaders valves removed 2x 1/4 lines from unit to gauges, then a 3/8 line from gauges to vac pump for maximum effect if you only got a small set of gauges= 3 x 1/4 fittings , you can fit a 1/4 femail 3/8 male addaptor to the middle 1/4 outlet to screw your 3/8 pipe to get the same effect.
    any comments ?
    11,025
    You can always remove the Schraeder cores to improve the vacuum experience.
    Apr 2008
    215
    I agree with Sedgy, use 4-valve manifold set with 3/8 hose for vac. Can always put remaining 2 or even 3 x 1/4 hoses on system without worrying about any restrictions.
    Use 2-valve sets for taking readings, etc.
    Dec 2009
    New zealand
    22
    Hi, There are some other small basics to keep in mind for reaching good evacuation levels. Using correct size and stage of vaccum pump on different capacity, changing oil after every use to reduce contamination of pump and vaccum gauges, keeping the o rings on your manifold hoses wet with lubricant so they dont wear quickly and seal to give good vaccum levels.
    Split Croatia
    57
    6,151
    36
    I see lot of different answers and some misconceptions.
    Check this document:
    http://www.mediafire.com/?zmyztx5gnzm
    Mar 2009
    La Piedad, Mexico
    38
    93
    Huge contribution in deed... I read it and help me a lot, know am searchin for 4 way mainflod, 3/8" ... or meaby 1/2" inch... IOL
    Somerset
    69
    4,713
    Everyone should take the time to read Nike's post.
    I Quote "
    Exactly how much does the size of the hoses effect conductance speed? The easy answer is BY A FACTOR OF 4! Which
    doesn't mean very much unless I add this bit of information; for every 1/8 Inch increase in hose size! That's right, for every
    1/8 Inch increase in hose size the conductance speed is increased by a factor of 4!"
    So in simple English.
    Increasing the hose size by 1/4" makes achieving your vacuum 4 times faster.
    Not any lower than the pump can achieve but faster.
    Nice one! Nike. ( Sorry I am not allowed to give you points at the moment. I must spread the warmth around apparently.)
    Auckland
    74
    3,357
    38
    The bigger the pipe and the shortest pipe will increase flow to vac pump. Most pumps are rated on free flow rating, not flash below zero pressure.
    Oct 2005
    IRAN
    878
    Hi guys,
    I just wanted to share these files.
    BTW : Vacuum is a very strange science, isn't it?
    PS : Sorry the file name spelling is incorrect !!!
    Attached Files Attached Files
    Even Einstein Asked Questions
  1. micron to mm
    By sparo in forum Fundamentals
    Last Post: 05-01-2009, 11:11 AM
  2. Oil Filter micron
    By Iceehot in forum NH3
    Last Post: 26-09-2008, 02:49 AM
  3. accepable levels using a Micron gauge
    By kengineering in forum Commercial
    Last Post: 06-12-2007, 11:50 AM
  4. Humidifiers with 1 micron droplet size
    By sharshal in forum Technical Discussions
    Last Post: 11-05-2007, 07:35 PM
  5. English readings
    By Lc_shi in forum Chit Chat & Service Stories
    Last Post: 19-01-2006, 09:12 AM