lowering micron readings
Hi Was thinking of purchasing 3/8" vacuum hoses . I was told this would speed up evacuation and get me a lower micron reading. But the hoses will still attache to 1/4" schrader valves with 3/16" openings. Mostly work on split systems and 10 ton or less roof top units. Wonder what you guys think. Thank you
Randy
-
17-04-2010, 02:10 AM #2
-
17-04-2010, 02:38 AM #3
Re: lowering micron readings
thanx but will I get a lower micron reading with the larger hoses?
-
17-04-2010, 11:18 AM #4
Re: lowering micron readings
My tutor at college had an old manual that said an increase in hose diameter decreases the evacuation time also that every time you double the length of the hose you double the evacuation time. As regards to lowering the micron reading hose daiameter is irrelavant as time and a good vac pump are the only factors in this also as Cool Runnings said triple vac is the best way of getting a good vacuum
-
17-04-2010, 12:10 PM #5
Re: lowering micron readings
No..
You will only get a lower Micron reading if the vac pump can pull that low (and as long as the system is gas tight).
No mater what size pipe you vac with you will pull a low vacuum, but the pipe will affect the speed so if you want to vac a system in a few mins you need a hugh vac pump and hugh pipes!! If you have hours to vac out you will always achieve the same level, only time will vary!!
A tripple vac is the way to go..
cool runnings.
.
-
17-04-2010, 01:13 PM #6
Re: lowering micron readings
Thank you guys you have saved me a few bucks
-
17-04-2010, 02:03 PM #7
Re: lowering micron readings
hi , just read your coments , I allways understud the vacing situation as=2 shaders valves removed 2x 1/4 lines from unit to gauges, then a 3/8 line from gauges to vac pump for maximum effect if you only got a small set of gauges= 3 x 1/4 fittings , you can fit a 1/4 femail 3/8 male addaptor to the middle 1/4 outlet to screw your 3/8 pipe to get the same effect.
any comments ?Last edited by sedgy; 17-04-2010 at 02:06 PM. Reason: very poor spelling1/10
-
17-04-2010, 11:23 PM #8
Re: lowering micron readings
You can always remove the Schraeder cores to improve the vacuum experience.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
17-04-2010, 11:37 PM #9
Re: lowering micron readings
I agree with Sedgy, use 4-valve manifold set with 3/8 hose for vac. Can always put remaining 2 or even 3 x 1/4 hoses on system without worrying about any restrictions.
Use 2-valve sets for taking readings, etc.
-
18-04-2010, 01:17 AM #10
Re: lowering micron readings
Hi, There are some other small basics to keep in mind for reaching good evacuation levels. Using correct size and stage of vaccum pump on different capacity, changing oil after every use to reduce contamination of pump and vaccum gauges, keeping the o rings on your manifold hoses wet with lubricant so they dont wear quickly and seal to give good vaccum levels.
-
18-04-2010, 11:13 AM #11
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: lowering micron readings
I see lot of different answers and some misconceptions.
Check this document:
http://www.mediafire.com/?zmyztx5gnzm
-
28-10-2010, 04:43 PM #12
-
30-10-2010, 08:19 AM #13
Re: lowering micron readings
Everyone should take the time to read Nike's post.
I Quote "
Exactly how much does the size of the hoses effect conductance speed? The easy answer is BY A FACTOR OF 4! Which
doesn't mean very much unless I add this bit of information; for every 1/8 Inch increase in hose size! That's right, for every
1/8 Inch increase in hose size the conductance speed is increased by a factor of 4!"
So in simple English.
Increasing the hose size by 1/4" makes achieving your vacuum 4 times faster.
Not any lower than the pump can achieve but faster.
Nice one! Nike. ( Sorry I am not allowed to give you points at the moment. I must spread the warmth around apparently.)
Grizzly
-
31-10-2010, 01:51 AM #14
Re: lowering micron readings
The bigger the pipe and the shortest pipe will increase flow to vac pump. Most pumps are rated on free flow rating, not flash below zero pressure.
-
02-11-2010, 03:41 AM #15
Re: lowering micron readings
Hi guys,
I just wanted to share these files.
BTW : Vacuum is a very strange science, isn't it?
Cheers
PS : Sorry the file name spelling is incorrect !!!Even Einstein Asked Questions
Similar Threads
-
micron to mm
By sparo in forum FundamentalsReplies: 12Last Post: 05-01-2009, 11:11 AM -
Oil Filter micron
By Iceehot in forum NH3Replies: 16Last Post: 26-09-2008, 02:49 AM -
accepable levels using a Micron gauge
By kengineering in forum CommercialReplies: 24Last Post: 06-12-2007, 11:50 AM -
Humidifiers with 1 micron droplet size
By sharshal in forum Technical DiscussionsReplies: 12Last Post: 11-05-2007, 07:35 PM -
English readings
By Lc_shi in forum Chit Chat & Service StoriesReplies: 1Last Post: 19-01-2006, 09:12 AM