    Smile lowering micron readings



    Hi Was thinking of purchasing 3/8" vacuum hoses . I was told this would speed up evacuation and get me a lower micron reading. But the hoses will still attache to 1/4" schrader valves with 3/16" openings. Mostly work on split systems and 10 ton or less roof top units. Wonder what you guys think. Thank you
    Randy



  2. #2
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: lowering micron readings

    Quote Originally Posted by Randykissling View Post
    Hi Was thinking of purchasing 3/8" vacuum hoses . I was told this would speed up evacuation and get me a lower micron reading. But the hoses will still attache to 1/4" schrader valves with 3/16" openings. Mostly work on split systems and 10 ton or less roof top units. Wonder what you guys think. Thank you
    Randy

    3/8 shared to your gauge manifold will increase the speed of the vac, slightly.

    But speed is not always best. Depth of vac or a good tripple vac is better than a fast evacuation.

    cool runnings

    .

  3. #3
    Join Date
    Mar 2010
    Location
    USA
    Age
    64
    Posts
    7
    Rep Power
    0

    Re: lowering micron readings

    thanx but will I get a lower micron reading with the larger hoses?

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: lowering micron readings

    My tutor at college had an old manual that said an increase in hose diameter decreases the evacuation time also that every time you double the length of the hose you double the evacuation time. As regards to lowering the micron reading hose daiameter is irrelavant as time and a good vac pump are the only factors in this also as Cool Runnings said triple vac is the best way of getting a good vacuum

  5. #5
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: lowering micron readings

    Quote Originally Posted by Randykissling View Post
    thanx but will I get a lower micron reading with the larger hoses?

    No..

    You will only get a lower Micron reading if the vac pump can pull that low (and as long as the system is gas tight).

    No mater what size pipe you vac with you will pull a low vacuum, but the pipe will affect the speed so if you want to vac a system in a few mins you need a hugh vac pump and hugh pipes!! If you have hours to vac out you will always achieve the same level, only time will vary!!

    A tripple vac is the way to go..

    cool runnings.

    .

  6. #6
    Join Date
    Mar 2010
    Location
    USA
    Age
    64
    Posts
    7
    Rep Power
    0

    Re: lowering micron readings

    Thank you guys you have saved me a few bucks

  7. #7
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: lowering micron readings

    hi , just read your coments , I allways understud the vacing situation as=2 shaders valves removed 2x 1/4 lines from unit to gauges, then a 3/8 line from gauges to vac pump for maximum effect if you only got a small set of gauges= 3 x 1/4 fittings , you can fit a 1/4 femail 3/8 male addaptor to the middle 1/4 outlet to screw your 3/8 pipe to get the same effect.
    any comments ?
    Last edited by sedgy; 17-04-2010 at 02:06 PM. Reason: very poor spelling1/10

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: lowering micron readings

    You can always remove the Schraeder cores to improve the vacuum experience.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: lowering micron readings

    I agree with Sedgy, use 4-valve manifold set with 3/8 hose for vac. Can always put remaining 2 or even 3 x 1/4 hoses on system without worrying about any restrictions.
    Use 2-valve sets for taking readings, etc.

  10. #10
    Join Date
    Dec 2009
    Location
    New zealand
    Posts
    22
    Rep Power
    0

    Re: lowering micron readings

    Hi, There are some other small basics to keep in mind for reaching good evacuation levels. Using correct size and stage of vaccum pump on different capacity, changing oil after every use to reduce contamination of pump and vaccum gauges, keeping the o rings on your manifold hoses wet with lubricant so they dont wear quickly and seal to give good vaccum levels.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: lowering micron readings

    I see lot of different answers and some misconceptions.
    Check this document:
    http://www.mediafire.com/?zmyztx5gnzm

  12. #12
    Join Date
    Mar 2009
    Location
    La Piedad, Mexico
    Age
    38
    Posts
    93
    Rep Power
    16

    Re: lowering micron readings

    Quote Originally Posted by nike123 View Post
    I see lot of different answers and some misconceptions.
    Check this document:
    http://www.mediafire.com/?zmyztx5gnzm

    Huge contribution in deed... I read it and help me a lot, know am searchin for 4 way mainflod, 3/8" ... or meaby 1/2" inch... IOL

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: lowering micron readings

    Everyone should take the time to read Nike's post.
    I Quote "
    Exactly how much does the size of the hoses effect conductance speed? The easy answer is BY A FACTOR OF 4! Which
    doesn't mean very much unless I add this bit of information; for every 1/8 Inch increase in hose size! That's right, for every

    1/8 Inch increase in hose size the conductance speed is increased by a factor of 4!"

    So in simple English.
    Increasing the hose size by 1/4" makes achieving your vacuum 4 times faster.
    Not any lower than the pump can achieve but faster.

    Nice one! Nike. ( Sorry I am not allowed to give you points at the moment. I must spread the warmth around apparently.)
    Grizzly

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: lowering micron readings

    The bigger the pipe and the shortest pipe will increase flow to vac pump. Most pumps are rated on free flow rating, not flash below zero pressure.

  15. #15
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: lowering micron readings

    Hi guys,

    I just wanted to share these files.

    BTW : Vacuum is a very strange science, isn't it?

    Cheers

    PS : Sorry the file name spelling is incorrect !!!
    Attached Files Attached Files
    Even Einstein Asked Questions

Similar Threads

  1. micron to mm
    By sparo in forum Fundamentals
    Replies: 12
    Last Post: 05-01-2009, 11:11 AM
  2. Oil Filter micron
    By Iceehot in forum NH3
    Replies: 16
    Last Post: 26-09-2008, 02:49 AM
  3. accepable levels using a Micron gauge
    By kengineering in forum Commercial
    Replies: 24
    Last Post: 06-12-2007, 11:50 AM
  4. Humidifiers with 1 micron droplet size
    By sharshal in forum Technical Discussions
    Replies: 12
    Last Post: 11-05-2007, 07:35 PM
  5. English readings
    By Lc_shi in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 19-01-2006, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •