    Piping design question



    I have an application that needs to select suction , discharge & liquid pipe sizes :

    The application is as follows :

    a) multi temp rack
    Evap temp : ( 27) deg C ,
    cONDENSING TEMP : 40 DEG c
    Comp capacity : 52 KW
    Refrigerant : R-404a
    Suction header selected : 64 mm , discharge header : 35 mm
    b) Ante-room
    Copm cap : 65 kw
    Evap : (-3) deg C
    CONDENSING TEMP : 40 DEG c
    R-404A
    Suction line 54 mm , dis line 42 mm



    Both these systems will be operated by three semi-hermetic compressors each with a compressor having 122.2 meter cub per hour displacement

    Question is :
    Individual system (a) & (b) suction / discharge pipe selected are given above .

    But how to calculate suction & discharge header sizes when all three compressors are connected to a common suction & discharge headers ?



  2. #2
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping design question

    Evap temp is -27 deg in the first application & not 27 deg c as mentioned

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Piping design question

    Based on ASHRAE tables, 67mm suction is suitable for 54kW @ -30°C evaporating temperature, while 35mm discharge is only suitable for capacities up to 41kW. I would suggest to use 42mm wide pipe.

    For the ANTE, I would suggest 54mm for the suction and 42mm for the discharge.

    Common headers shall have the same speed than individual pipes, so the cross section must be triple (for a three compressor multipack).

    35mm --> 67mm
    42mm --> 76mm
    54mm --> 105mm
    67mm --> 105 or 130mm

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Piping design question

    Hi,

    What is the pipe length and number of fittings?
    Is there suction or discharge vertical risers?
    Is there capacity control, if so what is the minimum capacity?

    For the common suction line you have to consider full load capacity then calculate the correct size.

    Cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping design question

    Thanks , nonickname !

    All three compressors will be connected to a common discharge & suction headers . Individual compressors will have indepedent oil separator, suction accumulator , oil reservoir and oil level regulator for each compressor through an oil filter .

    Appreciate your response !

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping design question

    Hi lana,

    all compressors will operate on capacities between 80 to 100% . The water cooled condenser will be mounted on frame work ; in other words the discharge piping will not be more than about 4 to 5 meters .
    I had selected pipe sections through a solken software .

    Thanks for your response !

  7. #7
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Piping design question

    Hi there,

    My calculation shows the followings :

    First system : suction 67mm and discharge 35mm.

    Second system : suction 54mm and discharge 28mm.

    Cheers
    Even Einstein Asked Questions

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping design question

    Hi lana ,
    thanks . However all the compressors will be connected to a common suction & discharge header . Hence the question prtains to how to work out a common header size with multi temp application . Each system will have its own mass flow ; -27 deg c & -3 deg c systems in this example ; but need to connect all the compressors to a common header , suction & discharge .
    Any suggestion how to proceed ?

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Piping design question

    How do you intend to controll rooms temp and defrost?

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping design question

    We are offering only the rack system i.e. High side equipment to the customer . The low side evaporator coil will have electrical defrost & coils will operate through tex valves with individual capacities & settings .as a rack provider , not much info is disclosed to rack designer .

  11. #11
    Join Date
    Jan 2010
    Location
    Southern California
    Posts
    19
    Rep Power
    0

    Smile Re: Piping design question

    Sir,

    If you are only supplying the rack, the lengths of piping you are dealing with are minimal. Size them for the total capacity of all compressors. Oversizing them slightly won't hurt, but undersizing them will cause unwanted pressure drops under full load conditions.

    You're no "Alfred Einstien" are you?

    Jeff P.

  12. #12
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: Piping design question

    Get a copy of TRANE "Reciprocating Refrigeration", Chapter 14, Refrigeration Piping. This provides copper tubing and pipe sizing as a function of refrigerant type and tonnage for liquid, suction, and hot gas piping as well as oil return requirements and recommendations. Another source is the Carrier Refrigeration Handbook, Piping Section. These charts, for whatever refrigerant you are using, are probably available on line.

  13. #13
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping design question

    Thanks Zpoint . We normally allow the loss of pressure in suction line since pipe lenghts are not really known to the designer . Hence 1 deg k penalty on suction may not be sufficient . Besdies, a size higher is offered for suction piping .

  14. #14
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Piping design question

    dougheret0,
    Thanks !
    However , do not know whether these two handbooks can be sourced . Any suggestion how to access these two books ?

Similar Threads

  1. HVAC piping design software
    By NoNickName in forum Fundamentals
    Replies: 26
    Last Post: 06-02-2010, 06:29 AM
  2. It is good piping design ?
    By oilzee in forum Trouble Shooting
    Replies: 6
    Last Post: 13-10-2008, 06:34 AM
  3. Piping Design Manual
    By ErnieA in forum NH3
    Replies: 21
    Last Post: 16-06-2008, 08:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •