    What are the requirements for testing or replacement of relief valves in refrigeration service. These are inline valves with NB stamps usually manufactured by Henry or Mueller?
  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19
    Re: Relief Valve Maintnenace Requirements
    Henry recomonends replacing their valves every five years also the larger chiller manufactures state the same
  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21
    valves need to be relaced every five years
  4. #4
    allpro's Avatar
    allpro Guest
    i have seen these valve last 10 years but, it needs to replace every 5
  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21
    insurance companys ask for them to be replaced every 5 years
  6. #6
    Join Date
    Mar 2008
    Location
    Glasgow
    Posts
    5
    Rep Power
    0
    Hi guys
    I work for Henry and keep a look out in this site for any issuse i can help with.
    I have seen our valves last about 10yrs, BUT we recommend changing every 5 yrs. this is in line with EN13136 Refrig standards. Also note some isurance companies say to change every 3 yrs.
Similar Threads
  1. Replies: 3
    Last Post: 26-08-2009, 09:37 AM
  2. LEV does not open
    By Yuri B. in forum Air Conditioning
    Last Post: 19-07-2009, 02:37 PM
  3. Oversize Relief Valve
    By Dacosta in forum NH3
    Last Post: 05-09-2008, 11:35 AM
  4. Carbo Cooler relief valve
    By flasah in forum NH3
    Last Post: 24-06-2006, 09:31 AM
  5. Relief Valve on Suction
    By Latte in forum Commercial
    Last Post: 20-01-2004, 11:57 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts