    Ammonia liquid carryover to screw compressor



    We have wrecked a compressor for liquid carryover. OEM says separator and suction piping sizing is perfect. Basically says operation or ammonia load was wrong.
    Question is : how to check carryover calculation ? I mean checking the separator sizing and/or vapor speed in the suction line.
    2nd question is : what is the right protection for the equipment in case OEM is right ? is suction superheat a good protection ? What should be the value ?

    This is a York, chiller PAC 128 HR, rotatune compressor with frequency variator, cooling water from 14,5°C to 9°C, 490 MCal/hr capacity.



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Ammonia liquid carryover to screw compressor

    Hi, mariano-arg

    Quote Originally Posted by mariano-arg View Post
    We have wrecked a compressor for liquid carryover. OEM says separator and suction piping sizing is perfect. Basically says operation or ammonia load was wrong.
    Question is : how to check carryover calculation ? I mean checking the separator sizing and/or vapor speed in the suction line.
    2nd question is : what is the right protection for the equipment in case OEM is right ? is suction superheat a good protection ? What should be the value ?

    This is a York, chiller PAC 128 HR, rotatune compressor with frequency variator, cooling water from 14,5°C to 9°C, 490 MCal/hr capacity.
    yes, I've been there ... whatever is delivered by OEM always is perfect ....so you made mistake and you will pay for it ... otherwise they have to pay for mistake ... very simple

    what about protection devices? which control you have on that unit UNISAB II or another?

    it is possible that you charge too much ammonia, but in that case you have protection devices which will stop compressor

    but, then if your control device setup was wrong ....?

    Give us some more data, please.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Nov 2008
    Location
    Argentina
    Posts
    14
    Rep Power
    0

    Re: Ammonia liquid carryover to screw compressor

    thank you Josip,

    Yes, control panel is Unisab II.
    It does not have any obvious protection against liquid carryover. It does not have a level switch, for instance. It does not have any liquid sensor in the suction line, or anything else that could "boil" liquid between separator and compressor.
    Suction pressure interlock is set up over 8 kg/cm2.
    Suction superheat is set up at 0,5°C. Trips off the unit if set up over this value.
    Discharge gas superheat is set up at 20°C w/5 minutes delay.
    Other standard protections, but nothing obvious to protect from liquid carryover.
    What could be a good protection ?

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Ammonia liquid carryover to screw compressor

    Does it have a suction trap in suction line ?
    Normally a high level float to protect it entering compressor .
    If its critacally charged suction trap should hold any excess refrigerant if TX valves fail .
    Could be overcharged ?
    Last edited by RANGER1; 14-04-2010 at 09:41 PM.

  5. #5
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Ammonia liquid carryover to screw compressor

    Suction superheat is set up at 0,5°C. Trips off the unit if set up over this value.
    Discharge gas superheat is set up at 20°C w/5 minutes delay.
    Other standard protections, but nothing obvious to protect from liquid carryover.


    This is protection from liquid carryover. It sounds like the unit is overcharged or you have a very high return water temperature at start up. This can cause the ammonia in the evaporator to "burp" and slug the compressor.

  6. #6
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: Ammonia liquid carryover to screw compressor

    Mariano:

    Carryover could be a cascade of problems.
    Please look at my small contribution. PAC-chiller

    ...
    Last edited by josei; 15-04-2010 at 02:14 PM.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Ammonia liquid carryover to screw compressor

    Quote Originally Posted by josei View Post
    Mariano:

    Carryover could be a cascade of problems.
    Please look at my small contribution. PAC-chiller

    ...
    Interesting link there Josei.
    I am on my way out of the door but will read more when I get back.
    Thanks.
    Grizzly

  8. #8
    piyush_ramani's Avatar
    piyush_ramani Guest

    Re: Ammonia liquid carryover to screw compressor

    Can anyone have any idea about to design Low pressure receiver,or selection programme,

  9. #9
    Join Date
    Nov 2008
    Location
    Argentina
    Posts
    14
    Rep Power
    0

    Re: Ammonia liquid carryover to screw compressor

    Charlie n, low suction gas superheat should trip off the compressor, trying to catch liquid carryover. What is a good value for this protection ? half degree looks too close to the saturation curve.

    Josei, interesting poing, by looking at the sight glass of the NH3 tank I can see some foam in the surface. Is this foam normal and expected ?

    There is no trap in the suction line. There is no level switch in the suction line, nor in the NH3 tank.

    This suction line is 4" starting horizontal and then down to the compressor. Compressor swept volume is up to about 1,500 Nm3/hr. What is the maximum velocity that this line should have to avoid droplets carryover?

  10. #10
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Ammonia liquid carryover to screw compressor

    Hi, mariano-arg

    Quote Originally Posted by mariano-arg View Post
    thank you Josip,

    Yes, control panel is Unisab II.
    It does not have any obvious protection against liquid carryover. It does not have a level switch, for instance. It does not have any liquid sensor in the suction line, or anything else that could "boil" liquid between separator and compressor.
    Suction pressure interlock is set up over 8 kg/cm2.
    Suction superheat is set up at 0,5°C. Trips off the unit if set up over this value.
    Discharge gas superheat is set up at 20°C w/5 minutes delay.
    Other standard protections, but nothing obvious to protect from liquid carryover.
    What could be a good protection ?

    What about alarms ... check measured values


    Sabroe sometimes advice to put SH to 0K only for this kind of chiller with PHE ... strange but truth, in that case your suction superheat protection is deactivated .... otherwise your compressor will stop very often ..., but there is another better protection by discharge superheat....


    There in UNISAB II version 2.05 is protection for liquid slugging warning and alarm ...

    ... warning is issued by a sudden decrease in discharge temperture which is greater then default 5C for a fixed 5 second period...

    .... alarm is issued by a sudden decrease in discharge temperature which is greater then default 10C for a fixed 5 second period.

    Then we have some other tools to regulate capacity, run time, timers for delay up or down, suction ramp etc... but that is not easy to explain here

    Finally, first start up should be done by York supervisor and he must write down all set points i.e. values .... also take care about ammonia charging .... happen like that or not

    UNISAB II is the most powerful PLC for regulation and control of refrigeration compressors, but set up must be OK.... otherwise is waste of money

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  11. #11
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Ammonia liquid carryover to screw compressor

    Mariano-arg, Josip has pretty well answered the question you had for me. The PAC chillers have flooded evaporators. The theoretical suction superheat is 0. Setting the suction superheat trip at 0.5 gives very little protection but if your superheat is higher, the chiller is undercharged or the PHE is fouled with oil. Discharge superheat is a better protection but neither will protect from an overcharged chiller. I installed and serviced several Sabroe PHE based chillers in the 90's before they had the pretty name (PAC) and before they got the oil return worked out. Some had no indication of liquid level so I would charge the unit with ammonia based on superheat. High superheat .. not enough charge. 1 degree superheat .. OK. For service ... high superheat .. oil in the Plate exchanger.
    Last edited by charlie n; 16-04-2010 at 12:58 AM. Reason: spelling mistakes

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Ammonia liquid carryover to screw compressor

    slow down the capacity load rate, to stop boil up in accumulator and carry over to compressor.
    magoo

  13. #13
    Join Date
    Nov 2008
    Location
    Argentina
    Posts
    14
    Rep Power
    0

    Re: Ammonia liquid carryover to screw compressor

    Quote Originally Posted by charlie n View Post
    Mariano-arg, Josip has pretty well answered the question you had for me. The PAC chillers have flooded evaporators. The theoretical suction superheat is 0. Setting the suction superheat trip at 0.5 gives very little protection but if your superheat is higher, the chiller is undercharged or the PHE is fouled with oil. Discharge superheat is a better protection but neither will protect from an overcharged chiller. I installed and serviced several Sabroe PHE based chillers in the 90's before they had the pretty name (PAC) and before they got the oil return worked out. Some had no indication of liquid level so I would charge the unit with ammonia based on superheat. High superheat .. not enough charge. 1 degree superheat .. OK. For service ... high superheat .. oil in the Plate exchanger.
    charlie n :
    Ok, I accept it. Theoretical superheat is 0. I put it in manual mode and the unit runs 2 to 3°C superheat. Makes me comfortable. The minute I put it to run in AUTO mode, the capacity fluctuations makes superheat go to under 1°C. If I was running close to 0°C what would happen to superheat when capacity changes ??
    It would hit the zero !! would that mean it is carrying droplets ??

  14. #14
    Join Date
    Nov 2008
    Location
    Argentina
    Posts
    14
    Rep Power
    0

    Re: Ammonia liquid carryover to screw compressor

    Quote Originally Posted by Josip View Post
    Hi, mariano-arg
    There in UNISAB II version 2.05 is protection for liquid slugging warning and alarm ...

    ... warning is issued by a sudden decrease in discharge temperture which is greater then default 5C for a fixed 5 second period...

    .... alarm is issued by a sudden decrease in discharge temperature which is greater then default 10C for a fixed 5 second period.

    Then we have some other tools to regulate capacity, run time, timers for delay up or down, suction ramp etc... but that is not easy to explain here

    .
    .
    .
    Best regards, Josip
    Josip, that kind of protection is exactly what I am looking for. I have Unisab II, don't know the version. How do I turn this function on ??

  15. #15
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Ammonia liquid carryover to screw compressor

    Hi, mariano-arg

    Quote Originally Posted by mariano-arg View Post
    Josip, that kind of protection is exactly what I am looking for. I have Unisab II, don't know the version. How do I turn this function on ??


    Version you can read from UNISAB II and settings are described in UNISAB II manual ... you should have it!?!

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  16. #16
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Ammonia liquid carryover to screw compressor

    Quote Originally Posted by mariano-arg View Post
    charlie n :
    Ok, I accept it. Theoretical superheat is 0. I put it in manual mode and the unit runs 2 to 3°C superheat. Makes me comfortable. The minute I put it to run in AUTO mode, the capacity fluctuations makes superheat go to under 1°C. If I was running close to 0°C what would happen to superheat when capacity changes ??
    It would hit the zero !! would that mean it is carrying droplets ??
    Mariano, I think you answered your own question. A lot of the problem is most likely coming from the load fluctuation. Take a look at this side of the system & try to find a way to buffer the load variations. Buffer tank or mixing valve or similar.
    You can also try to slow down the load/unload rate of the compressor. As I remember Unisab, you can widen the P band and you could reduce the oil feed to the slide valve by closing the needle valve a little.
    I wouldn't be comfortable with 3 degrees superheat. it sounds too high for a flooded evaporator.

  17. #17
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: Ammonia liquid carryover to screw compressor

    Sorry for my ignorance, but I have never encountered a ammonia system without a suction accumulator with a high level float switch or electronic level sensor. Is this design, without the safeties, common?

  18. #18
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: Ammonia liquid carryover to screw compressor

    Quote Originally Posted by chilldis View Post
    Sorry for my ignorance, but I have never encountered a ammonia system without a suction accumulator with a high level float switch or electronic level sensor. Is this design, without the safeties, common?
    Chilldis,

    Look at bottom pictures. PAC chiller with suction acumulator.

    As can see, HL switch not rqrd, bcause max. level ammonia (exagerated) is given by amount of liquid (critical) in system.
    As any flooded system is always wet, not superheated.
    This model produced by Sabroe-York-Frick, has sold thousands a.o.the.world.
    Screw compressor + UNISAB, best to capacity control from minimun to 100% volumen.

    Attached Images Attached Images
    Last edited by josei; 30-04-2010 at 02:04 PM.

  19. #19
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: Ammonia liquid carryover to screw compressor

    Thank-you for the education Josei. That just proves that a person only stops learning when they are dead. thanks again.
    Last edited by chilldis; 02-05-2010 at 03:25 AM. Reason: poor spelling skills

  20. #20
    Join Date
    Dec 2008
    Location
    usa
    Age
    83
    Posts
    34
    Rep Power
    0

    Re: Ammonia liquid carryover to screw compressor

    I am a late comer to this board but all you guys have good thoughts and comments. I would only add that if the slopover is not due to rapid load increases causing "old faithful" to errupt then it is very likely that there is too much oil in the PHE. Note this is where all the oil that escapes the compressor oil separator will eventually end up. Do you keep track of how much oil you add to the system? Do you remove the oil from the PHE and record the amount? Does system have an automatic oil return system to get the oil back to the compressor that does not work? Years ago I had a trouble shoot job where the owner had added oil for 20 years to an old recip ammonia flooded shell and tube evaporator. He did not know he had to manually drian the oil and the evaporator was 1/2 full of oil. Approximately 300 gallons oil were removed from the flooded evap..

Similar Threads

  1. Grasso - 9 cylinder Compressor - Ammonia
    By rlmts in forum Industrial Compressors
    Replies: 24
    Last Post: 04-10-2010, 07:39 PM
  2. YORK Rotary Screw Compressor
    By xelazman in forum Industrial Compressors
    Replies: 7
    Last Post: 28-04-2010, 08:37 PM
  3. Liquid in compressor when charging
    By Mish in forum Trouble Shooting
    Replies: 7
    Last Post: 09-03-2009, 08:08 PM
  4. Autoloading slide valve for Screw compressor
    By screw_geek in forum Industrial Compressors
    Replies: 32
    Last Post: 04-04-2008, 03:47 AM
  5. Oil Pump in Ammonia Compressor?
    By NNNNNN in forum Technical Speculations
    Replies: 22
    Last Post: 05-03-2008, 12:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •