    Mitsubishi 4108 fault



    Hi,

    I have this fault code on a City Multi, I know the fault is something to do with the fixed speed compressor tripping on overload, does anybody know how to get this compressor to run manually so I can check out the run current, i've checked the windings and they are OK.

    Cheers



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Mitsubishi 4108 fault

    Try giving mitsi technical a ring 01707282880
    you could also try putting a feed to the contactor coils or simply push the contactor in,also have you checked the comp is getting all three phases ie fuses mains supply
    hope this helps

  3. #3
    Join Date
    Sep 2009
    Location
    UK
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi 4108 fault

    Hi,

    Cheers for the info, the only problem is you have to disconnect all the wires from the main board to open the panel and get to the contactors and overload, I've checked the contactor & Overload for continuity and thats OK, I don't want to power the unit up with the main board disconnected.

    I'll try Mitsubishi tomorrow.

    Cheers

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Mitsubishi 4108 fault

    the only other way i can think of is if you have an amp clamp with a peak hold function on is to put your lamp on,reset the fault, run the unit and repeat for all three phases

  5. #5
    Join Date
    Sep 2009
    Location
    UK
    Posts
    22
    Rep Power
    0

    Re: Mitsubishi 4108 fault

    Thanks for that James, I'll give that a go.

    Cheers

  6. #6
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi 4108 fault

    As the windings are ok the compressor could be locked or a problem with the contactor + overload.
    I dont think there is any setting on the outdoor unit to bypass or over ride the contactor overload. But the overload is connected to the relay board on most of the larger PUHY-P YMF-C units so you should be able to measure if the overload is operating or not from the relay board & that is on the front panel next to the control board.
    You could do a ' no load' test by disconnect the 3 power cables at the compressor. make safe by connecting to a blank terminal block & then run system. Measure the voltage at each 240v power supply cable & 3ph between.
    This could give an indication of a problem with the contactor or overload.

    If you are brave then make a direct connection from the outdoor unit isolator to the compresor direct.
    If the compressor runs at high amps then there is some mechanical problem with the compressor.
    If the compressor trips the power supply MCB back at the distributon board then the compressor is locked.
    As the MCB should be sized for the system with inverter compressor & fan running & fixed speed compressor starting then if you only direct connect the fixed speed compressor to the power supply the MCB should not trip & the compressor should start & run.
    Dont run the compressor like this for more than a few seconds because all the valves in the system will be shut & the discharge pressure will rise very fast & with it the compressor amps.
    So take start amps & run amps after a few seconds & then switch off.

    Disclaimer / safety warning
    Only do this direct on line test if you are qualified & confident working with 3ph as it can kill

Similar Threads

  1. Mitsubishi fault code 4108
    By boulting in forum Air Conditioning
    Replies: 4
    Last Post: 23-12-2009, 01:23 PM
  2. mitsubishi heavy industries fault
    By skeggyboy in forum Air Conditioning
    Replies: 3
    Last Post: 20-08-2009, 06:41 PM
  3. Mitsubishi fault MUZ-A09
    By coffeebreak in forum Trouble Shooting
    Replies: 0
    Last Post: 11-07-2009, 05:50 PM
  4. Mitsubishi Electric Intermittent fault
    By marc5180 in forum Air Conditioning
    Replies: 28
    Last Post: 15-01-2009, 10:19 PM
  5. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •