    Chiller water information



    Hi all,
    can anyone help
    We have an air cooler chiller with a closed looped system wtih chill water pumps and 4- 40 ton air handler units.

    I have having some heat exchange problems That I cannot seem to solve.

    I have water leaving at 45 degrees and returning at 48 to 50 degrees.

    I have sox ducts on the AHU which tend to drop I have done a full coil cleaning and can say the coil is clear and air passes through. I cannot remmeber the CFM of the unit at the momnet but last it was checked it was with in range.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Chiller water information

    Why do you think its a heat exchange problem?

    For that matter, what makes you think there is a problem?
    Last edited by Gary; 13-04-2010 at 04:20 PM.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Chiller water information

    We need more info to help on this one like - air on, air off, supply outlet temp, chwv position and chwbypass position. Is it a VAV or FAV?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller water information

    Quote Originally Posted by ronsin1 View Post

    I have water leaving at 45 degrees and returning at 48 to 50 degrees.

    I have sox ducts on the AHU which tend to drop
    Did I correctly understood that you have flexible (textile) ducts from air handling units which "tend to drop"? What this "tend to drop" mean?
    Check fans rotation direction and proper air flow!
    Last edited by nike123; 14-04-2010 at 09:34 AM.

  5. #5
    ronsin1's Avatar
    ronsin1 Guest

    Re: Chiller water information

    Quote Originally Posted by nike123 View Post
    Did I correctly understood that you have flexible (textile) ducts from air handling units which "tend to drop"? What this "tend to drop" mean?
    Check fans rotation direction and proper air flow!
    all the system I deal with are fabric duct systems. The unit that is in question use to have the ducts firm. now they are not firm as they use to be.

    The fan rotation is correct I have check that already it moves in a clock wise direction as how it always is

    Gary it has to be a heat exchange problem on the evaporator coil. I have a good water supply temp.

    with this temp I should have an ambient temp inside the building of 71F but I o not have that I have more like 79 which is to high.

    I have another building with the same system an do not have these issues

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Chiller water information

    What controls the temps?

    Is the AHU multizone or single zone?

    Face/bypass air dampers?

    Chill water bypass?

    What are the water pressures?

    What is the system elevation?

    We need to know more about the AHU.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller water information

    Quote Originally Posted by ronsin1 View Post
    all the system I deal with are fabric duct systems. The unit that is in question use to have the ducts firm. now they are not firm as they use to be.
    To me that indicate that air flow across unit is less than before. Less air flow mean less heat gain at AHU and therefore delta T of water at evaporator is smaller and capacity of unit is lowered.
    Measure your airflow. Check with manufacturer data for proper airflow.
    If fan motors are mono-phase, check capacitors for correct capacity.

Similar Threads

  1. low evaporator chiller water flow & chiller water overdue alarm
    By jurekorgurek in forum Trouble Shooting
    Replies: 4
    Last Post: 02-08-2009, 10:34 AM
  2. Need help in Building water chiller.
    By Bluestar in forum Technical Speculations
    Replies: 6
    Last Post: 30-12-2008, 06:20 AM
  3. Beer Chiller Motor/Mixer
    By fredrick_more in forum Commercial
    Replies: 36
    Last Post: 13-10-2008, 06:45 PM
  4. Is there a 24V water chiller? Around 300W?
    By wilsonudevil in forum Fundamentals
    Replies: 4
    Last Post: 27-08-2008, 01:43 PM
  5. water chiller
    By dwallan in forum Air Conditioning
    Replies: 3
    Last Post: 12-12-2001, 03:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •