    Question Remote fitted condensing unit



    Hi Everyone.
    If the condensing unit of a refrigeration system is remote fitted, how is it accounted in component selection?. For example a walk-in cold room with heat load of, say 4000 BTUH, has to be constructed either with the condensing unit attached to it or the unit 10 m (32.8 ft) away. If the condensing unit is away will it use the same condensing unit as that of the first case? Or how is it selected.
    Thanks in advance

    With regards
    Rayin



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Remote fitted condensing unit

    Hi there,

    The distance between components is used to size the pipes. With the correct length of the pipes and its fittings the pipe size must be calculated for pressure drop and oil return to the compressor.

    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Remote fitted condensing unit

    The size of the condenser will not change unless you have much higher or lower temperatures outside than inside.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Remote fitted condensing unit

    As previous posters already said, size is not dependent on distance, it depend on conditions of air which is around condenser.
    If your condenser is designed for indoor usage with temperatures from 10°C to 30°C it cannot be used for outdoor where temperatures are from -5°C to 45°C or more.

  5. #5
    Join Date
    Nov 2006
    Location
    Middle East (United Arab Emirates)
    Posts
    43
    Rep Power
    0

    Re: Remote fitted condensing unit

    Hi..Lana, Peter_1 and Nike,
    Thank you for your prompt response. So from your rplies what I understand is, as far as ambient air condition is not changed, no need to change the condensing unit, for a remote fitted unit. Only thing the pipe line sould be sized in such a way that the total pressure loss should be in the permissible limit of design conditions. Am I correct?

    Cheers
    Rayin

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Remote fitted condensing unit

    Indeed Rayin, just calculate your lines, that's all.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Nov 2006
    Location
    Middle East (United Arab Emirates)
    Posts
    43
    Rep Power
    0

    Re: Remote fitted condensing unit

    Dear Peter_1,
    It is clear now. Thank you very much indeed.
    Cheers
    Rayin

Similar Threads

  1. DX capacity lower than condensing unit
    By M.Saleh in forum Air Conditioning
    Replies: 2
    Last Post: 18-01-2010, 03:01 AM
  2. Sizing a condensing unit for a serve over counter
    By jimbo22 in forum Fundamentals
    Replies: 0
    Last Post: 25-11-2009, 04:50 PM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM
  4. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •