why A/Cs are not installing inside battery rooms. Here we have so many battery rooms, A/Cs are installed in seperate room and only opening for supply air and exhaust fan used for air flow. Please give some technical clarifications.
14-04-2010, 05:35 AM #2
14-04-2010, 06:41 AM #3
Re: battery room A/Cs
yes grizzly,
You are absolutely correct, but I need to know what type of explosive gases are forming while on battery charging. I have to give a report against this.
Thank you
14-04-2010, 09:34 AM #4
Lead Acid batteries give off Hydrogen when charging, and, being heavier than air, low level trickle ventilation should be installed to prevent accumulation and the risk of explosion.
14-04-2010, 08:22 PM #5
Frank I think you meant to type in lighter rather than heavier. As Hydrogen is lighter than air. I would assume that any vents should be on the high spots in the room. All electrical devices would be explosion proof. vinod Just look at any videos of the Hindenburg on fire to see the danger of Hydrogen gas. C.D.
NH3 for me
14-04-2010, 08:55 PM #6
Thank you CD
I've always installed battery room ventilation with the extract at low level next to the batteries with the make up air coming from the opposite wall at high level, causing a positive flow of fresh air across the room.
I looked up what our H & S Executive recommends and here is the link.
http://www.hse.gov.uk/pubns/indg139.pdf
Looks like I've been doing it back to front for some years....
19-04-2010, 07:59 AM #7
freezer room equipment
By jack smith in forum Tools and CalculatorsReplies: 4Last Post: 12-06-2010, 05:27 AM -
Blind Cold room specs help
By frostedflake in forum Trouble ShootingReplies: 5Last Post: 13-03-2009, 01:49 AM -
Heat transfer coefficient - Coolpack
By Graham in forum FundamentalsReplies: 10Last Post: 28-05-2008, 01:08 AM -
Freezer Room Panels
By Feeze in forum Technical DiscussionsReplies: 10Last Post: 22-04-2005, 05:58 AM