    Question battery room A/Cs
    why A/Cs are not installing inside battery rooms. Here we have so many battery rooms, A/Cs are installed in seperate room and only opening for supply air and exhaust fan used for air flow. Please give some technical clarifications.
    4,698
    Re: battery room A/Cs
    Quote Originally Posted by vinod View Post
    Hi Vinod.
    Just a wild guess!
    But at times during charging Certain Battery types can give off Explosive Gases
    Hence the reason for the remote A/C unit, I am assuming?
    Dec 2005
    uae
    54
    yes grizzly,
    You are absolutely correct, but I need to know what type of explosive gases are forming while on battery charging. I have to give a report against this.
    Thank you
    5,668
    Lead Acid batteries give off Hydrogen when charging, and, being heavier than air, low level trickle ventilation should be installed to prevent accumulation and the risk of explosion.
    Jul 2008
    wet coast B. C.
    122
    Frank I think you meant to type in lighter rather than heavier. As Hydrogen is lighter than air. I would assume that any vents should be on the high spots in the room. All electrical devices would be explosion proof. vinod Just look at any videos of the Hindenburg on fire to see the danger of Hydrogen gas. C.D.
    NH3 for me
    5,668
    Thank you CD
    I've always installed battery room ventilation with the extract at low level next to the batteries with the make up air coming from the opposite wall at high level, causing a positive flow of fresh air across the room.
    I looked up what our H & S Executive recommends and here is the link.
    http://www.hse.gov.uk/pubns/indg139.pdf
    Looks like I've been doing it back to front for some years....
    Dec 2005
    uae
    54
    Thank you CD
    Thanks for all to given me such a clear advice and information
  1. Replies: 12
  2. freezer room equipment
    By jack smith in forum Tools and Calculators
    Last Post: 12-06-2010, 05:27 AM
  3. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Last Post: 13-03-2009, 01:49 AM
  4. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Last Post: 28-05-2008, 01:08 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Last Post: 22-04-2005, 05:58 AM