    Question battery room A/Cs



    why A/Cs are not installing inside battery rooms. Here we have so many battery rooms, A/Cs are installed in seperate room and only opening for supply air and exhaust fan used for air flow. Please give some technical clarifications.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: battery room A/Cs

    Quote Originally Posted by vinod View Post
    why A/Cs are not installing inside battery rooms. Here we have so many battery rooms, A/Cs are installed in seperate room and only opening for supply air and exhaust fan used for air flow. Please give some technical clarifications.
    Hi Vinod.
    Just a wild guess!
    But at times during charging Certain Battery types can give off Explosive Gases
    Hence the reason for the remote A/C unit, I am assuming?
    Grizzly

  3. #3
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: battery room A/Cs

    yes grizzly,
    You are absolutely correct, but I need to know what type of explosive gases are forming while on battery charging. I have to give a report against this.
    Thank you

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: battery room A/Cs

    Lead Acid batteries give off Hydrogen when charging, and, being heavier than air, low level trickle ventilation should be installed to prevent accumulation and the risk of explosion.

  5. #5
    Join Date
    Jul 2008
    Location
    wet coast B. C.
    Age
    76
    Posts
    122
    Rep Power
    16

    Re: battery room A/Cs

    Frank I think you meant to type in lighter rather than heavier. As Hydrogen is lighter than air. I would assume that any vents should be on the high spots in the room. All electrical devices would be explosion proof. vinod Just look at any videos of the Hindenburg on fire to see the danger of Hydrogen gas. C.D.
    NH3 for me

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: battery room A/Cs

    Thank you CD

    I've always installed battery room ventilation with the extract at low level next to the batteries with the make up air coming from the opposite wall at high level, causing a positive flow of fresh air across the room.

    I looked up what our H & S Executive recommends and here is the link.
    http://www.hse.gov.uk/pubns/indg139.pdf

    Looks like I've been doing it back to front for some years....

  7. #7
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: battery room A/Cs

    Quote Originally Posted by frank View Post
    Thank you CD

    I've always installed battery room ventilation with the extract at low level next to the batteries with the make up air coming from the opposite wall at high level, causing a positive flow of fresh air across the room.

    I looked up what our H & S Executive recommends and here is the link.
    http://www.hse.gov.uk/pubns/indg139.pdf

    Looks like I've been doing it back to front for some years....
    Thanks for all to given me such a clear advice and information

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. freezer room equipment
    By jack smith in forum Tools and Calculators
    Replies: 4
    Last Post: 12-06-2010, 05:27 AM
  3. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  4. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •