    Evap fans spinning the wrong way?



    I got sent to a site today to fit a new evap fan motor on a walk in cooler on R22 since the old one had burnt out.

    There are 2 evap fans side by side i only replaced the one of them.

    After i had replaced the fan and switched it on i noticed that the fans were not pulling the air from the back of the coil and blowing it out into the room but were in fact pulling the air from the room over the motor and onto the coil, with the airflow coming out of the back of the coil and blowing onto the coldroom wall which was about 8 inches away (see picture)

    Since the airflow was blowing onto the wall, i noticed that even after a few hours the wall had become dirty (see pic)

    The fans are single phase anti clockwise rotation fans and are going the way that they are made but i think they shouldn't have anti direction motors fitted.

    I understand that the fans should run counter flow to the refrigerant but i don't think they do.

    Anyone ever come across this?
    Attached Images Attached Images
    Last edited by marc5180; 13-04-2010 at 09:57 PM.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Evap fans spinning the wrong way?

    I think the evap has been fitted the wrong way round, lots of those little evaps blow through the coil whereas all the big ones suck through, looks like a searle unit, have a word with climate technical tomorrow and see.

    Jon

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Evap fans spinning the wrong way?

    I agree with MS, unit mounted the wrong way round.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Evap fans spinning the wrong way?

    In the old days it was often done to fit the evap to blow against the back wall. It stopped the cold dry air blowing directly onto the produce

    The evap is a searle the fan guards are the clue. If you've fixed it I would move on as it's been like that for years.

  5. #5
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Evap fans spinning the wrong way?

    3+1, Cooler fitted wrong way round. It'll work, just have crap air distribution in the room. Tell them to make sure the area around the cooler is clear & keep the door shut..

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Evap fans spinning the wrong way?

    Well thats a new one to me.

    It did seem to cool the room down and all the pressures/temps were fine but the fact that the back wall was gtting dirty was something that made me question it.

    As suggested i'll leave it be.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evap fans spinning the wrong way?

    They are spining as they supposed to spin. As others alredy said, evaporator is fited 180° wrong way and fans side should be near cold-room wall as on this picture.



    You could fit evaporator properly or try to reverse fan rotation direction by changing main and auxilary winding on condenser (if they have same resistance) but I am not sure that that will produce same air flow across evaporator, and I am sure that air distribution in cold-room will be very bad in upper portion of cooler. If it is positive temperature, some air deflectors could be fited to direct air flow upwards.
    Last edited by nike123; 14-04-2010 at 08:37 AM.

  8. #8
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: Evap fans spinning the wrong way?

    Yep, its been put up the wrong way round
    In the words of David Byrne, Well...How did I get here?

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Evap fans spinning the wrong way?

    The easy way to reverse it is to get fan blades with the reverse pitch... but I would leave it as is.

  10. #10
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Evap fans spinning the wrong way?

    Quote Originally Posted by Gary View Post
    The easy way to reverse it is to get fan blades with the reverse pitch... but I would leave it as is.
    dont change anything thats the way they were fit in the old days . start messing around with blades . just asking for problems .

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Evap fans spinning the wrong way?

    Quote Originally Posted by tony--1 View Post
    thats the way they were fit in the old days .
    You are kidding! Or you not?
    Who, whit at least ounce of brain, will fit evaporator to blow air directly in wall behind evaporator.
    That was fitted by some moron who saw evaporator like that first time in his life, and was so much blind that can not be able to see mounting instructions which coming inside packaging and was acting by his "rich experience" since all "normal" evaporators are fitted with fans at front of evaporator.

    Thanks Good that "old days " are history now! Or did they not?
    Last edited by nike123; 19-04-2010 at 06:12 AM.

Similar Threads

  1. Electronic controller probes wired wrong
    By Electrocoolman in forum Trouble Shooting
    Replies: 3
    Last Post: 12-11-2007, 06:39 PM
  2. iced up evap coil
    By wilks in forum Fundamentals
    Replies: 6
    Last Post: 31-08-2007, 09:15 PM
  3. TK SB III SRTCI Evap fans
    By reefermadness in forum Transport
    Replies: 2
    Last Post: 27-04-2007, 12:20 AM
  4. Eveporator Fans Tripping
    By Feeze in forum Trouble Shooting
    Replies: 26
    Last Post: 21-02-2005, 06:10 AM
  5. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Replies: 13
    Last Post: 04-12-2003, 04:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •