    General Fault...again.



    Just been to look at General unit (ABG24RBA, I think). As soon as the unit is powered up it goes straight in to fault.

    Operation (red) flashes 2 times
    Timer (Green) Flashes rapidly
    Vertical Swing (Orange) Flashes rapidly
    Horizontal Swing is off all the time.

    I donīt have any manuals or codes or anything for this unit, but I think that is Room Thermistor Fault, am I right?

    cheers,
    paul..



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: General Fault...again.

    Check your model #!

  3. #3
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: General Fault...again.

    The data plate is pretty mashed up and hard to read. Itīs a floor/ceiling unit on R22 I think. It might be ABG24RBA-W, is that any closer?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: General Fault...again.

    Yep it is probably room thermistor error. It should be 10kOhm at 25°C.

  5. #5
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: General Fault...again.

    thanks Nike, is that model nš correct?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: General Fault...again.

    Quote Originally Posted by airefresco View Post
    thanks Nike, is that model nš correct?
    Yes it is! Old ceiling R22 noninverter model!

  7. #7
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: General Fault...again.

    That sounds right, many thanks.

  8. #8
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: General Fault...again.

    I know this is quite an old thread but I have just been to do this job. Swapped the sensor over, powered up and and the unit started. Switched the power off and back on again and then unit now goes in to pipe thermistor fault before the outdoor even starts.

    I think it is a dead PCB as the client didn't tell me before, but if they turned the power off to the unit, when turned back on it would sometimes (1 out of 10 times) work until the power went off again, at which point it would show the room thermistor fault. So it seems to be an intermittent fault, hence why I think indoor PCB.

    Any thoughts?

Similar Threads

  1. Supra common fault - usually misdiagnosed.
    By carrier_trained in forum Transport
    Replies: 3
    Last Post: 15-04-2010, 08:56 PM
  2. Daikin Split f3 Fault
    By moondawn in forum Air Conditioning
    Replies: 18
    Last Post: 01-06-2009, 07:09 PM
  3. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM
  4. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  5. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •