10-04-2010, 05:33 AM #1
Grasso compressors & cooling towers / condensers relationship
What difference / setback / plus point - will it make if we install the condensers / cooling towers at the same level as that of compressors instead of putting them up at 3500 mm level.
My problem is that the contractor wants it to be 3500 mm above ground whereas I would like it to be at ground level main reason being high construction costs for a 50 Ft x 20 Ft. platform.
I will appreciate suggestions that can be helpful to place the condensers / cooling towers at ground level.
The contractor has the following comments:
1-After condensation liquid flows from condenser always by gravity with certain slope to avoid the liquid trapping in lines .
2-Condenser should always in open Air for optimized condensation process (ITS IN THE OPEN AIR ALREADY)
3-There should always be a certain pressure in liquid receiver at out let of condenser to avoid the vaporization in liquid receiver .
4- From Process design point of view Grasso strongly recommends that condenser should always be placed at certain height
-
10-04-2010, 09:46 AM #2
Re: Grasso compressors & cooling towers / condensers relationship
Too difficult to give a clear answer without more details or drawings/location/process/climate information. Are you talking about a shell & tube condenser? The relationship between a condenser and receiver is more important. Condenser should always be above the receiver.The cooling tower location usually doesn't matter, it can be on the ground.
-
10-04-2010, 11:14 PM #3
Re: Grasso compressors & cooling towers / condensers relationship
From Process design point of view Grasso strongly recommends that condenser should always be placed at certain height
You have provided the reason for putting the condenser above ground level.
If the manufacturer recommends something then do it or invalidate your warranty with them.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-04-2010, 03:02 PM #4
Re: Grasso compressors & cooling towers / condensers relationship
hello
1 experience of towers below condensers meant water drained back then air lock problems. needs designed to prevent probs like this
aww
-
11-04-2010, 06:31 PM #5
Re: Grasso compressors & cooling towers / condensers relationship
I assume you have evaporative condensers.,I suggest you strictly follow the instructions of the "OEM" (Grasso) to avoid any problems during your operation. In ammonia refrigeration, evaporative condensers are always installed above the compressors and liquid receiver.
Similar Threads
-
cooling tower's free cooling issue
By Lc_shi in forum New TechnologiesReplies: 12Last Post: 30-01-2011, 04:41 AM -
Water cooling condensers
By FEISTY in forum Trouble ShootingReplies: 0Last Post: 28-03-2009, 01:48 AM -
Compressors - screw or reciprocating?
By Josip in forum Industrial CompressorsReplies: 18Last Post: 27-01-2009, 10:36 PM -
Cooling towers Vs Riverwater cooling
By Cammy in forum FundamentalsReplies: 7Last Post: 27-08-2008, 09:52 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM