Hitachi dc scroll failure
Hi All
I have a Hitachi RAC 2.5kW split that has been steadily reducing in capacity and now won't heat at all. Guages show reasonable static pressure for the temperature but very little rise in heating mode. Compressor is running (sound is normal and quiet) and can hear the inverter ramping up it's speed OK.
Most likely it's dead and uneconomic to repair but I wondered what kind of failure this has experienced?
Probably relevant - when new the system needed to be fitted with a crank-case heater since otherwise it would not start when cold outside.
Any thoughts greatly appreciated
Cheers
-
12-04-2010, 10:12 AM #2
Re: Hitachi dc scroll failure
hey jimbo what refrigerant is the system running? what were the refrigerant pressures whilst running?
-
12-04-2010, 12:09 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Hitachi dc scroll failure
It could be as simple as refrigerant leak.
Check charge by recovering refrigerant and weigh recovered amount. It must be within 1-2% of nameplate weight. If it is not in that range, you have leak which must be found and repaired and then unit should be charged by nameplate weight.
If it is in that range than you maybe have inefficient compressor or 4-way valve which has excessive leak rate.
-
21-04-2010, 10:38 PM #4
Re: Hitachi dc scroll failure
I had one doing the same recently in my own office. Just short on refrigerant. Working beautifully now. Whats the pipe run? Minimum run is 5 metres. This can cause problems. What is the model number?
Similar Threads
-
Carrier Transicold Container Problem
By Shamel in forum TransportReplies: 39Last Post: 23-01-2012, 11:23 PM -
Hitachi scroll compressors
By tonydeith in forum CommercialReplies: 3Last Post: 21-01-2011, 01:48 PM -
Digital Scroll VRF Systems & Inverter Systems
By weeliang82 in forum Air ConditioningReplies: 22Last Post: 16-11-2010, 04:07 PM -
scroll compressor failure
By sagar45 in forum Trouble ShootingReplies: 26Last Post: 07-06-2009, 03:56 PM -
Well Done / Thanks Hitachi UK
By Latte in forum Chit Chat & Service StoriesReplies: 4Last Post: 24-11-2008, 07:52 PM