    Hitachi dc scroll failure



    Hi All

    I have a Hitachi RAC 2.5kW split that has been steadily reducing in capacity and now won't heat at all. Guages show reasonable static pressure for the temperature but very little rise in heating mode. Compressor is running (sound is normal and quiet) and can hear the inverter ramping up it's speed OK.

    Most likely it's dead and uneconomic to repair but I wondered what kind of failure this has experienced?

    Probably relevant - when new the system needed to be fitted with a crank-case heater since otherwise it would not start when cold outside.

    Any thoughts greatly appreciated

    Cheers



  2. #2
    Join Date
    Jan 2010
    Location
    australia
    Age
    39
    Posts
    32
    Rep Power
    0

    Re: Hitachi dc scroll failure

    hey jimbo what refrigerant is the system running? what were the refrigerant pressures whilst running?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Hitachi dc scroll failure

    Quote Originally Posted by Jimbo! View Post

    Most likely it's dead and uneconomic to repair but I wondered what kind of failure this has experienced?
    It could be as simple as refrigerant leak.
    Check charge by recovering refrigerant and weigh recovered amount. It must be within 1-2% of nameplate weight. If it is not in that range, you have leak which must be found and repaired and then unit should be charged by nameplate weight.
    If it is in that range than you maybe have inefficient compressor or 4-way valve which has excessive leak rate.

  4. #4
    Join Date
    Feb 2005
    Location
    United Kingdom
    Age
    53
    Posts
    56
    Rep Power
    20

    Re: Hitachi dc scroll failure

    I had one doing the same recently in my own office. Just short on refrigerant. Working beautifully now. Whats the pipe run? Minimum run is 5 metres. This can cause problems. What is the model number?

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Hitachi scroll compressors
    By tonydeith in forum Commercial
    Replies: 3
    Last Post: 21-01-2011, 01:48 PM
  3. Digital Scroll VRF Systems & Inverter Systems
    By weeliang82 in forum Air Conditioning
    Replies: 22
    Last Post: 16-11-2010, 04:07 PM
  4. scroll compressor failure
    By sagar45 in forum Trouble Shooting
    Replies: 26
    Last Post: 07-06-2009, 03:56 PM
  5. Well Done / Thanks Hitachi UK
    By Latte in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 24-11-2008, 07:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •