    NH3 Piping



    G'day,

    Does anyone have info on selection/design of vent line from receiver to condenser in a thermosyphon system?

    regards



  2. #2
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: NH3 Piping

    You need this data:
    compressor cooling capacity and shaft power, also condensing and suction conditions.

    Procedure of sizing recommended by “Thermosyphon Oil Cooling,” guide from Frick-Imeco-York 1991

  3. #3
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: NH3 Piping

    This might help
    Attached Images Attached Images

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: NH3 Piping

    totally wierd question, receiver to condenser vent, with thermosyphon.
    Thermosyphon what? oil cooler perhaps. Please clarify.
    Thermo oil cooler oil side should be vented to compressor discharge, the liquid side should be vented to atmosphere. So requires two safety releif valves. To protect system from fire and some idiot that isolates the liquid side and liquid hydraulics the vessel.
    magoo

  5. #5
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: NH3 Piping

    yeah, pls. clarify your query GBRD.,why vent line from liquid receiver then back to condenser?,maybe non-condensible lines or relief valves from condenser & receiver.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: NH3 Piping

    I've seen a thermosyphon cooler of +/- 700 kW to precool cooked vegetables.
    Then this question isn't that weird at all Magoo
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: NH3 Piping

    @Charlie_N, may I ask, out of which book is this coming from?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: NH3 Piping

    Peter_1, The table is from ASHRAE Refrigeration Handbook, 2006

  9. #9
    Join Date
    Sep 2009
    Location
    Australia
    Posts
    41
    Rep Power
    0

    Re: NH3 Piping

    Hi Magoo, you seem to have got totally confused with this single line question. I'm talking of vent line FROM RECEIVER TO CODNENSER & not lines from safety valves etc.

  10. #10
    Join Date
    Sep 2009
    Location
    Australia
    Posts
    41
    Rep Power
    0

    Re: NH3 Piping

    Hi Ref717,

    You need vent line to keep receiver & condenser at same pressure & hence you try to equilize it through vent line. Its a must in a Thermosyphon Oil Cooling System, otherwise there could be issues like liquid drain from condenser to receiver & high system pressure...

    regards

  11. #11
    Join Date
    Sep 2009
    Location
    Australia
    Posts
    41
    Rep Power
    0

    Re: NH3 Piping

    Hi Josei,

    You seem on the right track mate, can you elaborate further if possible.

    regards

  12. #12
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: NH3 Piping

    I would have thought charlie n chart was pretty good under 'VENT' vent for t/syphon lubricant cooling .
    Also make it as big as possible as it can't hurt , only help .

  13. #13
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Smile Re: NH3 Piping

    yes GBRD you're definitely correct, we call this as the equalizing line.,this piping is required to relieve potential uneven pressure conditions inside the receiver. This pipeline is from the hot gas discharge line going to the top of the receiver tank as designed in our plant.We don't have a separate pilot receiver for the compressors' thermosyphon oil coolers.
    You can check the website of "EVAPCO" bulletin 131-E" for the correct piping procedures.
    I hope this aides you in your query..

    best regards..

  14. #14
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: NH3 Piping

    Quote Originally Posted by josei View Post
    You need this data:
    compressor cooling capacity and shaft power, also condensing and suction conditions.

    Procedure of sizing recommended by “Thermosyphon Oil Cooling,” guide from Frick-Imeco-York 1991
    GBRD:

    If You send data asked in my firt message Ill give you pipe diameter back.


    04-13-2010

    GBRD:

    I checked Frick´s calculations vs diameters shown in attached table[Evapco´s Vessel].
    Proximity of values is good enough for practical use.
    You must use value of heat rejected by compressor to be oil cooled.


    Josei
    Attached Images Attached Images
    Last edited by josei; 13-04-2010 at 06:58 PM.

  15. #15
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: NH3 Piping

    Quote Originally Posted by josei View Post

    04-13-2010

    GBRD:

    I checked Frick´s calculations vs diameters shown in attached table[Evapco´s Vessel].
    Proximity of values is good enough for practical use.
    You must use value of heat rejected by compressor to be oil cooled.


    Josei
    Please see this link..

Similar Threads

  1. Piping labels
    By duke717 in forum NH3
    Replies: 2
    Last Post: 29-04-2009, 02:57 AM
  2. cooling water piping system
    By 2007eng in forum Air Conditioning
    Replies: 3
    Last Post: 19-04-2009, 12:08 PM
  3. It is good piping design ?
    By oilzee in forum Trouble Shooting
    Replies: 6
    Last Post: 13-10-2008, 06:34 AM
  4. Q: Piping installation for Split Types
    By brianubaldo in forum Refrigerants
    Replies: 11
    Last Post: 30-04-2008, 02:23 PM
  5. Vibration in refrigerant piping
    By US Iceman in forum Technical Discussions
    Replies: 5
    Last Post: 01-05-2006, 11:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •