    Blast freezer addition



    As of now we have all our rooms (low temp) -5F running off the same engine room sharing the same suction accumulator and suction line. The question is we are thinking of changing one of the rooms to a blast freezer we have enough H.P to do so but do you think it would be a good idea to run this blast freezer on it's own suction line,accumulator and booster? We would like to see a temp of in the range of -30F thanx for any input and have a great day!



  2. #2
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Blast freezer addition

    Yes it is not advisable to run a blast freeze rm. with only a -5 deg.F system. Definitely you would not achieve the required blast frezer evap. temp. of -30 deg.F by just sharing with the -5 system. You need to design and install a new -30degF system with a new compressor,aircooler,surge accumulator with pumps and an intercooler/economizer.

Similar Threads

  1. Air blast freezer designation - limited space
    By Sien in forum Industrial
    Replies: 5
    Last Post: 14-12-2009, 10:13 AM
  2. Blast Freezer Within Freezer
    By rickmor in forum Technical Discussions
    Replies: 4
    Last Post: 18-06-2009, 03:37 AM
  3. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM
  4. Blast Freezer
    By w.l.ong in forum Industrial
    Replies: 17
    Last Post: 16-12-2006, 10:34 AM
  5. Blast Freezer Questions
    By rickmor in forum Industrial
    Replies: 2
    Last Post: 11-04-2006, 08:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •