    Obstructed Capillary Tubes



    I have been finding more cases recently of obstructed cap tubes on commercial equipment. All have been with R-134a or R-404a refrigerant. I don't know if it is the POE oil causing the problem. The obstruction is usually partial, causing high superheat. This often causes frosting of the evaporator and ultimately leads to compressor failure. I found a couple of threads relating to a similar problem on domestic refrigerators. The consensus for domestics was to dispose of the refrigerator and buy a new one. That isn't practical with more expensive commercial equipment. Is anyone else noticing these problems?



  2. #2
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Obstructed Capillary Tubes

    Hi terrygoodrich,welcome to RE
    Had this problem a few times .I usually try clearing restriction with nitrogen (OFN)flushing or cutting back capillary tube.One other method is to islolate electrically, reclaim any refrigerant, unsweat suction from compressor,disconnect cap at drier and purge from either side of drier and up the disconnected suction into the coil.
    Failing everything if accesible replace the whole capillary according to manufactures recommended length.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Obstructed Capillary Tubes

    Hi Terry,

    The combination of R-134a + POE oil cleans everything from inside the copper tubes and the result is obstruction in the cap tube.

    I used to do as Mark did but no more. always replacing the cap tube.
    Sometimes, I would choose a bigger diameter one and work out the length.


    Chemi

  4. #4
    Join Date
    Jul 2001
    Location
    Northern New York
    Age
    62
    Posts
    42
    Rep Power
    0

    Re: Obstructed Capillary Tubes

    Replacing the cap tube is often a difficult task the way these cases are assembled. Why don't the filter-driers prevent whatever is fouling the cap tubes from getting in there in the first place?... and why don't the manufacturers use larger diameter tubes if that solves the problem? I have installed expansion valves on some ice cream cabinets that are particularly susceptible to compressor damage from high superheat. This isn't an easy task either! I just wanted to get a feel for the extent of the problem out there. I'm sure compressor manufacturers are feeling the pinch from compressor failures under warranty. That will fuel the fire for a solution. Thanks for the replies guys!
    Last edited by terrygoodrich; 10-03-2005 at 12:45 AM. Reason: PS

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Obstructed Capillary Tubes

    Why don't the filter-driers prevent whatever is fouling the cap tubes from getting in there in the first place?...
    With R134a it's the oil that waxes and blocks the capillary. No filter will prevent this.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Obstructed Capillary Tubes

    With R134a it's the oil that waxes and blocks the capillary
    At what temp doe's it wax? Or is it happening all the time?

    S***t refrigerant

    Chemi

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Obstructed Capillary Tubes

    Have a look at this old thread Chemi http://www.refrigeration-engineer.co...read.php?t=458

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Obstructed Capillary Tubes

    There was life before I came

    To be honest, I hated it the second time I've used it, Back in the last century.

    Dont tell anybody, but I retrofit to R-12.

    It works so much better

    Chemi

  9. #9
    Join Date
    Jul 2001
    Location
    Northern New York
    Age
    62
    Posts
    42
    Rep Power
    0

    Re: Obstructed Capillary Tubes

    I can't see how the refrigerant could cause the blockage. The solids must be coming from the oil or a combination of oil and moisture. The solids are being deposited in the capillary tube immediately after the filter-drier. It doesn't seem to matter what brand of filter is used. I suspect the solids are in solution and precipitate out as the refrigerant pressure and temperature drop through the cap tube. That is the only way they could get through the filter. Is there a chemist in the forum?

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Obstructed Capillary Tubes

    Believe me, its the R-134a that causes all the problems

    Chemi

Similar Threads

  1. Selection of capillary tubes
    By patrickj in forum Commercial
    Replies: 11
    Last Post: 19-06-2008, 02:45 PM
  2. capillary tubes
    By JimmyMurphy in forum Fundamentals
    Replies: 2
    Last Post: 24-06-2006, 07:49 AM
  3. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  4. Replies: 15
    Last Post: 24-10-2002, 06:52 PM
  5. Capillary Tubes
    By subzero*psia in forum Domestic
    Replies: 19
    Last Post: 26-06-2001, 11:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •