    I have been finding more cases recently of obstructed cap tubes on commercial equipment. All have been with R-134a or R-404a refrigerant. I don't know if it is the POE oil causing the problem. The obstruction is usually partial, causing high superheat. This often causes frosting of the evaporator and ultimately leads to compressor failure. I found a couple of threads relating to a similar problem on domestic refrigerators. The consensus for domestics was to dispose of the refrigerator and buy a new one. That isn't practical with more expensive commercial equipment. Is anyone else noticing these problems?
    Jun 2002
    628
    Re: Obstructed Capillary Tubes
    Hi terrygoodrich,welcome to RE
    Had this problem a few times .I usually try clearing restriction with nitrogen (OFN)flushing or cutting back capillary tube.One other method is to islolate electrically, reclaim any refrigerant, unsweat suction from compressor,disconnect cap at drier and purge from either side of drier and up the disconnected suction into the coil.
    Failing everything if accesible replace the whole capillary according to manufactures recommended length.
    Sep 2003
    ISRAEL
    72
    4,248
    Hi Terry,
    The combination of R-134a + POE oil cleans everything from inside the copper tubes and the result is obstruction in the cap tube.
    I used to do as Mark did but no more. always replacing the cap tube.
    Sometimes, I would choose a bigger diameter one and work out the length.
    Chemi
    Jul 2001
    Northern New York
    42
    Replacing the cap tube is often a difficult task the way these cases are assembled. Why don't the filter-driers prevent whatever is fouling the cap tubes from getting in there in the first place?... and why don't the manufacturers use larger diameter tubes if that solves the problem? I have installed expansion valves on some ice cream cabinets that are particularly susceptible to compressor damage from high superheat. This isn't an easy task either! I just wanted to get a feel for the extent of the problem out there. I'm sure compressor manufacturers are feeling the pinch from compressor failures under warranty. That will fuel the fire for a solution. Thanks for the replies guys!
    5,667
    With R134a it's the oil that waxes and blocks the capillary. No filter will prevent this.
    Sep 2003
    ISRAEL
    72
    4,248
    At what temp doe's it wax? Or is it happening all the time?
    S***t refrigerant
    Chemi
    5,667
    Have a look at this old thread Chemi http://www.refrigeration-engineer.co...read.php?t=458
    Sep 2003
    ISRAEL
    72
    4,248
    There was life before I came
    To be honest, I hated it the second time I've used it, Back in the last century.
    Dont tell anybody, but I retrofit to R-12.
    It works so much better
    Chemi
    Jul 2001
    Northern New York
    42
    I can't see how the refrigerant could cause the blockage. The solids must be coming from the oil or a combination of oil and moisture. The solids are being deposited in the capillary tube immediately after the filter-drier. It doesn't seem to matter what brand of filter is used. I suspect the solids are in solution and precipitate out as the refrigerant pressure and temperature drop through the cap tube. That is the only way they could get through the filter. Is there a chemist in the forum?
    Sep 2003
    ISRAEL
    72
    4,248
    Believe me, its the R-134a that causes all the problems
    Chemi
  1. Selection of capillary tubes
    By patrickj in forum Commercial
    Last Post: 19-06-2008, 02:45 PM
  2. capillary tubes
    By JimmyMurphy in forum Fundamentals
    Last Post: 24-06-2006, 07:49 AM
  3. metric capillary tube
    By tralex in forum Fundamentals
    Last Post: 21-02-2006, 06:57 AM
  4. Replies: 15
    Last Post: 24-10-2002, 06:52 PM
  5. Capillary Tubes
    By subzero*psia in forum Domestic
    Last Post: 26-06-2001, 11:56 PM