    Hello
    Can some body please tell me if it is possible to work out the flow rate on a chilled water system with a binder gauge and how do you calculate it in ltrs/min
    Many Thanks



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Working out chilled water flow rates

    you need to measure the pressure drop across the evaporator/condensor(difference between entering and leaving water pressures) on the bindi points then using the flow charts for the chiller you can work it out from them if you have the chiller model and serial i might be able to help you a bit more

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Working out chilled water flow rates

    Or....if you know the duty of the chiller and measure the dt between the flow and return, Q=mcdt will give you the mass flow rate.

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. water flow
    By jebar in forum Tools and Calculators
    Replies: 3
    Last Post: 15-04-2009, 07:42 PM
  3. Chilled water bypass problem
    By MACT in forum Trouble Shooting
    Replies: 5
    Last Post: 16-10-2008, 02:01 AM
  4. Comments on this please
    By Robearbam in forum Fundamentals
    Replies: 8
    Last Post: 18-04-2005, 05:20 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •