Results 1 to 22 of 22
    Mar 2010
    Bangladesh
    40
    151
    15
    Problem with chiller
    We are using HITACHI Chiller, Model No.: RCUP-46AU(Z). Refrigerent R 407 C.
    Our main problem is the chiller section sometimes tripped and fault shows 13-13 Active of freeze protection by thermistr.
    #Chilled water inlet temp. 10 Deg. C and outlet temp. 9 Deg. C.
    #We check the thirmistor.
    # Chilled water flow pressure is ok, and we also clean the evaporator (as described in manual) after the problem arrived.
    # Purge air from the chilled water line.
    Note: After cleaning the evaporator the chiller unit didnt tripped for a week, and after that it showing the same problem again.
    What is the probable troubleshooting steps now...............?
    11,025
    Re: Problem with chiller
    You say that the chilled water flow pressure is OK but is the flow rate correct?
    Also you are only showing 1°C across the evaporator, not very much happening there is there?
    Mar 2010
    Bangladesh
    40
    151
    15
    Sir,
    Thanks for the replay..........
    I have no idea how to measure flow rate across the evaporator, & most of the time chilled water inlet & outlet temperature difference is not less then 2 deg C.
    Mar 2010
    Dammam
    83
    15
    this is unusual,temp. difference across the evaporator should be around 6-9 deg. Celsius.,Brian_UK is correct,check the chilled water flowrate,maybe you dont have enough water velocity in the evaporator.,or there is ice-build up in the evaporator coils,check also your expansion valve.
    Apr 2001
    79
    5,071
    35
    I would start with the piping. The water should enter the bottom of the evaporator and exit the top.
    Apr 2001
    79
    5,071
    35
    Quote Originally Posted by Bashir01219 View Post
    Was there air in the chilled water line?
    Mar 2010
    Bangladesh
    40
    151
    15
    The water should enter the bottom of the evaporator and exit the top. Yes our chilled water system line have the facility.
    Oct 2008
    mallorca, spain,
    75
    768
    hi bashir, also is the chiller very old?, have you inspected the chilled water strainer?
    Mar 2010
    Bangladesh
    40
    151
    15
    we have strainer after pump but not before evaporator.
    Oct 2003
    5,630
    34
    Quote Originally Posted by ref717 View Post
    t...temp. difference across the evaporator should be around 6-9 deg. Celsius.,Brian_UK is correct,check the chilled water flowrate,maybe you dont have enough water velocity in the evaporator....
    If you should have not enough waterflow,then you will see a big DT,
    So in his case, waterflow is extremely high
    Where is freeze protection measurement located exactly?
    Mar 2010
    Bangladesh
    40
    151
    15
    How can we measure water flow? We can measure it through raw method, but is it error free.
    Parallel we have another Trane chiller, and there is no problem.
    And the position of the freeze protection sensor is chilled water outlet line.
    Apr 2001
    79
    5,071
    35
    Unless there is zero waterflow, in which case there should be zero dT.
    Apr 2001
    79
    5,071
    35
    You missed this question.
    Apr 2001
    79
    5,071
    35
    Chilled water flow pressure is ok...
    Ok is an opinion, not a pressure.
    What is the pressure?
    Mar 2010
    Bangladesh
    40
    151
    15
    Chilled water inlet pressure 4.8 Bar, & outlet pressure nearly 4.0 Bar.
    There is no air in the chilled water line, we check the air venting line several times.
    sometimes dT shows Zero, at the begining of the machine start.
    Aug 2009
    New Zealand
    2,554
    26
    Hi, do you know what your suction pressure/temp.
    Are you sure that the freeze sensor is in the water line, and not in a pocket in the evap.
    My gut feeling is that your tubes are fouled, stopping heat transfer, but not enough to block the flow. causing a lower SST than normal
    Mad F
    Apr 2001
    79
    5,071
    35
    What refrigerant is in the system?
    When the system is running, what are the pressures, temperatures, subcooling, superheat?
    When the system is off what pressure does it equalize at?
    Mar 2010
    Bangladesh
    40
    151
    15
    Sir, Lots of question?
    You know i am new in this line,
    Refrigerant: R407C,
    System need to run at 7.00 am to 8.00 pm (everyday).
    Temp. at TXV valve 17 deg C, Evaporating pressure 95 PSI
    Superheat temp. nearly 6 deg C.
    Compresser discharge pressure 340 PSI,
    Temperature leaving the condenser 53.1 deg C
    So, subcool temp. 3 deg C.
    Note: Parallel we have another Trane chiller.
  19. #19
    Aug 2009
    New Zealand
    2,554
    26
    Refrigerant: R407C,
    Good info, based upon this your water temp readings are wrong, your evap temp is higher than your water temp.
  20. #20
    Mar 2010
    Bangladesh
    40
    151
    15
    when i got the readings, chilled water temp. was in inlet 15 deg. C, & outlet 14 deg. C.
  21. #21
    Apr 2001
    79
    5,071
    35
    Your readings are still wrong. What are you measuring temperatures with?
  22. #22
    Mar 2010
    Bangladesh
    40
    151
    15
    From the panel i got the temp.
  1. problem with multistack chiller
    By bright in forum Refrigerants
    Last Post: 30-10-2010, 10:43 PM
  2. Problem with mcquay chiller
    By texanul in forum Industrial
    Last Post: 04-02-2010, 08:51 PM
  3. Problem with centrifugal chiller
    By engalmohannad in forum Commercial
    Last Post: 19-04-2009, 10:00 PM
  4. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Last Post: 01-07-2008, 06:05 PM
  5. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Last Post: 21-06-2008, 09:12 AM